A simple high side float can separate liquid from the reheat flow and bypass the secondary condenser. However, this is best suited for a parallel style system, and whereas this can be extremely simple solution where you only need a small portion of the total heat of rejection,(10 to 20%) it becomes very dificult to effectivly control when the heat rejection is greater than that.
The trick to the whole thing, is that there must be enough condensing surface somewhere to provide 100% condensing. No more... No less. Q=UA¦T
where Q is the heat rejected
U is the heat transfer coeficient of the heat exchanger,
A is the effective surface area
¦T is the difference between SDT and ambient (or liquid)
(this is simplified quite a bit but shows the overall relationship)
Therefore, if you want a higher condensing temperature, there must be less condensing area, or warmer condensing medium or both.
Most valve manufacturors, (Sporlan, ALco, Parker, Danfos etc) will show methods of doing this in their catalogues and which parts are required to achieve the desired results.
hope this helps.
Imok2
With a sufficiently intelegent control system this could work.
But the real secrets to these systems are
Q "where is the liquid refrigerant going to go"
A always to the colder spot
Q "where will the heat be rejected to?
A The heat will try to go to the coldest spot.
Q "how do I get the heat to go where I want it too.
A make the other condenser have a warmer temperature (cycle fans, close dampers, or smaller EFFECTIVE AREA, flood the tubes with liquid refrigerant, etc)
The secret to success is to know where your refrigerant chrg is going to go.