Concrete Cover For Retaining Wall?

Status
Not open for further replies.

psustruct

Structural
Joined
Dec 2, 2010
Messages
16
Location
US
If a retaining wall is permanently exposed to earth, shouldn't the concrete cover be 3"? Why am I seeing so many engineers use a 2" cover?
 
others will have better answers, but I believe you can use less cover if the wall is formed and the back-filled vs. cast directly against the earth with no forms.
 
ACI only requires a 3" cover for earth-formed structures. It is 2" for walls that cast against formwork and permanently exposed to earth.
 
yes, agree with steelion.

ACI says 3" cover for 'cast against and permanently exposed to earth'.

 
OK. Thank you for the clarification.
 