aggman
Structural
- Jun 9, 2003
- 253
I have a situation where I have two 30" X 42" concrete columns cantilevered up from a footing 25'. The contractor wants to pour the columns in 6' increments, leaving 3 construction joints in the footer. I looked in the ACI code and could not find anything that specifically said you could not do this, but my gut says that this would hinder the shear transfer in the column since the concrete would have a horizontal crack all the way through. The column sees realatively high shear and bending, while the compressive loads are small compared to the column size. This also makes me uneasy, due to the friction between the concrete faces would not be overly high, forcing the shear into the vertical bars. Reinforcement consist of 22 #8 bars vertical and #4 ties @ 10". What are your opinions on this? Please respond as soon as you can, as they are breathing down my back to give them an answer.
Thanks,
Thanks,