Concentrated Load on Wood Sheathing - plywood/osb
RFreund
I believe this has been asked before however there does not seem to be a definitive answer (or I didn't see it).
Does anyone have any examples/recomendations/referances for analysing a point load on plywood/osb floor.
I have found in the plywood specification that the punching shear may be the area of the point load x the perimeter. However how can bending and or deflection be addressed? Is there a reasonable tributary width to assume?
Thanks in advance.
EIT
try:
or
APA's "Plywood Design Specification"
The last paragraph of Section 3.8.1 (Shear thru thickness) states:
"Shear-thru-the-thickness values as given in Table 3 shall also be used for 'punching shear' calculations. However, no increases in allowable stress shall be taken for face grain orientation, glued frame reinforcement, or restricted core gaps."
PS 1-83:
"Section 4.5.5 states that the general provisions of ASTM E661 are to be followed."
boo - thanks for the response. However that thread and document are what I was referring to in OP. I just wanted to see if there was any other 'recommendations/design guides' out there.
EIT
See the following APA publications
E440 (garage floor loading addresses rolling concentrated wheel loads)
N375 (design capacities -read the whole thing)
TT-071 (more garage quick tech guide)
X227 (caster loading on plywood)
______________
MAP