Hokie93
Structural
- Sep 9, 2007
- 375
I am seeking opinions as to whether the provisions of ACI 318-11 12.14.2.3 can be applied to a column member that is solely in compression. ACI 318-11 12.14.2.3 states:
Bars spliced by nonontact lap splices in flexural members shall not be spaced transversely farther apart than the smaller of one-fifth the required lap splice length, and 6".
I have a situation where the dowel bars at the base of a cast-in-place concrete column need to be offset from the column longitudinal bars by approximately 3 inches. The fact that 12.14.2.3 specifically indicates noncontact lap splices are permitted in "flexural members" is giving me pause. I would not typically classify a column subject solely to compression as being a flexural member. I checked ACI 318 back to the 1989 version and the requirement is unchanged.
Bars spliced by nonontact lap splices in flexural members shall not be spaced transversely farther apart than the smaller of one-fifth the required lap splice length, and 6".
I have a situation where the dowel bars at the base of a cast-in-place concrete column need to be offset from the column longitudinal bars by approximately 3 inches. The fact that 12.14.2.3 specifically indicates noncontact lap splices are permitted in "flexural members" is giving me pause. I would not typically classify a column subject solely to compression as being a flexural member. I checked ACI 318 back to the 1989 version and the requirement is unchanged.