Question reponses as they came in -
Anchor Bolts: 2 3/4" Dia. A325 Anchor Bolts Specified with 12" embedment, cast-in-place, 3000 psi concrete, spaced 5" apart on each side of a 4" tube column. (Note: contractor placed 4 anchor bolts in compliance with OSHA requirements)
Obstructions: Just the 8" CMU walls on each side, concrete column is flush with outside face of wall.
Column Load- exact from calcs unknown (not my design, but another person from my firm) however this is a library and there is one story and a roof supported by the steel column. Floor system is a steel beam and joist system with concrete deck 3" total height on 1" 26 GA steel form. Approx 200 SF of trib area. My quick approx is around 25psf dead and 150 psf live(floor) and 20 psf live(roof). Thus, a total load of approx 45 kip.
CMU walls: 8" block with #4 @ 48" o.c., grouted only at reinforcing.