oengineer
Structural
- Apr 25, 2011
- 732
I have a question regarding minimum wall thicknesses for Circular Cast-In-Place Concrete Manholes. I am trying to specify a minimum wall thickness on the detail sheet. The Circular Cast-In-Place Concrete Manhole for the project has an interior diameter of 6 ft and the overall height of the manhole is 13 ft tall.
In the Design Data 20: Circular Precast Concrete Manholes from the American Concrete Pipe Association, it mentions the following criteria to determine the wall thickness:
The minimum wall thickness equals one-twelfth the inside diameter of the manhole, when the thinnest wall thickness specified in ASTM C76 is used.
Would it be acceptable to apply this criteria to a Circular Cast-In-Place Concrete Manhole? If not, is there another a available minimum wall thickness criteria to specifically address Circular Cast-In-Place Concrete Manholes?
Suggestions/comments are appreciated.
In the Design Data 20: Circular Precast Concrete Manholes from the American Concrete Pipe Association, it mentions the following criteria to determine the wall thickness:
The minimum wall thickness equals one-twelfth the inside diameter of the manhole, when the thinnest wall thickness specified in ASTM C76 is used.
Would it be acceptable to apply this criteria to a Circular Cast-In-Place Concrete Manhole? If not, is there another a available minimum wall thickness criteria to specifically address Circular Cast-In-Place Concrete Manholes?
Suggestions/comments are appreciated.