Can anyone describe the definitive method of carrying out this task? Is it as simple as placing the Clamp meter on the phases and matching this up to the nameplate on the pump?
You can measure electrical power at the motor (current and voltage), but you would need to convert to mechanical shaft HP at pump. You need to do a little more research for this. You have to account for motor efficiency:
For large and critical pumps, then consider a direct measurement of pump shaft torque and speed to get shaft HP. Check out Binsfeld wireless torque system. I have an older model.
Measuring power input doesn't really tell you much about the pump performance other than it's drawing more or less current - it's of use if used in conjunction with flow / head measurements.
It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)
recently i faced ampere issues on condenser pump, the full load amps was 90A, but draws only 40A. the site contractor even overhauled the pump, checked impeller size...etc. but the actual problem was the discharge butterfly valve was stuck....
At the motor terminals,or are we missing something?
It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)