Lionel; Was that set up as a torque motor to take up slack or was it inching operation.
Gee V/Hz = 0.01457, The rated voltage at 60 Hz = 4120 Volts
Probably inching a 4160 Volt motor for alignment. Too big for a torque motor.
columbo7 The thing is; when we ask the questions we understand the answers.
You have been lucky. We usually don't do this much teaching.
Many are bounced after the second or third post.
Be grateful for the help that you have been given.
p.s. Re the 100 Hz operation. that may be a trick more often used by compressor skid builders.
By running a motor at double voltage and double frequency, you double the HP.
This is sometimes done so as to use a smaller motor.
BUT
The manufacturer has to use a pump that will not overload the motor at 6000 RPM.
Yes, it can be done at the design stage, but you can not generally overspeed a centrifugal pump by very much.
And yes I have seen something similar done in a special case.
We needed a head of about 200 feet. The smallest pump capable of producing that head was much too large for the application.
The pump shop extrapolated a pump curve to find the RPM needed to develop the head required. They then calculated the HP required.
A suitable motor was selected and the pump was belt driven above the motor speed to get the 200 foot head.
That pump would normally have a motor of about 15 HP or 20 HP. At the increased speed, we needed 30 HP.
When you start talking about pump drives you must consider the pump as well as the motor.
Oh, and by the way, I haven't seen everything but 400 Volts @ 60 Hz is pretty rare in North America. What type of plant is this?
Bill
--------------------