EN50522 is the new European standard for earthing of power installations exceeding 1kV a.c.
The standard outlines the methodology to be followed to select appropriate touch and step voltage safety limits when designing high voltage substation earth grids (covered in Annex A and Annex B of the standard).
I would be interested in hearing from anyone using the new EN50522 standard regarding what touch voltage (and step voltage) limits are being used by different utilities, and how these are being calculated.
Although a 'default' plot of permissible touch voltages is shown in Figure 4 of the standard, showing touch voltage limits for a range of earth fault clearance times, it is not clear from the information presented in Annex A and Annex B of the standard exactly how this figure is derived. The standard suggests that "The curve in Figure 4, which gives the permissible touch voltage, should be used", although the Annexes also suggest that alternative limits can be derived using the methodology shown.
Figure B.2 (in Annex B) shows example touch voltage limits which have taken into account a range of different surface layer resistances (e.g. for different types of crushed rock) and footwear resistances. However, again it is not clear from the information provided exactly how these limits have been calculated. An "iterative process" is apparently used, but based on the limited information provided my colleagues have had difficulties in replicating the results shown in Figures 4 and B.2, let alone adapting these for different surface layer or footwear resistances.
I would welcome any comments or discussion based on the following:
(a) Are any utilities using the touch voltage limits based on the curve shown in Figure 4 of the EN50522 standard?
(b) Are any utilities using the touch voltage limits based on one (or more) of the curves shown in Figure B.2 in Annex B of EN50522?
(c) Are any utilities using alternative touch voltage limits calculated using the methodology shown in Annex A and Annex B of EN50522?
(d) Are any utilities using different criteria to determine step voltage limits, or are they simply assuming that the touch voltage limits provided in EN50522 also apply to step voltages (a conservative approach)?
Thanks in advance for any comments, and apologies for the length of the posting. It's my first post so I wanted to be thorough!
The standard outlines the methodology to be followed to select appropriate touch and step voltage safety limits when designing high voltage substation earth grids (covered in Annex A and Annex B of the standard).
I would be interested in hearing from anyone using the new EN50522 standard regarding what touch voltage (and step voltage) limits are being used by different utilities, and how these are being calculated.
Although a 'default' plot of permissible touch voltages is shown in Figure 4 of the standard, showing touch voltage limits for a range of earth fault clearance times, it is not clear from the information presented in Annex A and Annex B of the standard exactly how this figure is derived. The standard suggests that "The curve in Figure 4, which gives the permissible touch voltage, should be used", although the Annexes also suggest that alternative limits can be derived using the methodology shown.
Figure B.2 (in Annex B) shows example touch voltage limits which have taken into account a range of different surface layer resistances (e.g. for different types of crushed rock) and footwear resistances. However, again it is not clear from the information provided exactly how these limits have been calculated. An "iterative process" is apparently used, but based on the limited information provided my colleagues have had difficulties in replicating the results shown in Figures 4 and B.2, let alone adapting these for different surface layer or footwear resistances.
I would welcome any comments or discussion based on the following:
(a) Are any utilities using the touch voltage limits based on the curve shown in Figure 4 of the EN50522 standard?
(b) Are any utilities using the touch voltage limits based on one (or more) of the curves shown in Figure B.2 in Annex B of EN50522?
(c) Are any utilities using alternative touch voltage limits calculated using the methodology shown in Annex A and Annex B of EN50522?
(d) Are any utilities using different criteria to determine step voltage limits, or are they simply assuming that the touch voltage limits provided in EN50522 also apply to step voltages (a conservative approach)?
Thanks in advance for any comments, and apologies for the length of the posting. It's my first post so I wanted to be thorough!