Most of the industrial installations, the distribution is by cables. Therefore, there is no way for the GF current to pass through soil.
As an example, if there is a ground fault inside a motor installed 100m away from MCC, the GF current is taken back to the MCC by the
bonding conductor (in IEC cables by the armour or PE, in tray cables by the grounding conductor laid with the cable). Therefore, there is no
STEP, TOUCH, GPR to be calculated using the soil resistivity.
But at the same industrial installation, it may be fed by a 25kV distribution line terminated at a small substation consisting bkr, disco switch
etc etc. At that setup if there is a GF at the sub, then 99% of that GF current is taken back to the Utility source through the soil. That means,
if there is person standing on the soil of that substation he is subjected to STEP, TOUCH & GPR due to soil resistance. Hence the modeling should be done
per IEEE 80 knowing the soil resistivity & the max. GF current.