Just to add a bit of clarification to electricpete's post -- voltage in the formula is line-to-line voltage (which is the standard way of stating a three-phase voltage).
Power factor does not figure into the kVA - Amps conversion.
It only comes into play when determining kW.
Of course, a low power factor means there may be an opportunity to correct it (using capacitors or other means), which would lower the kVA to a value closer to the kW value while simultaneously lowering amperage.
Suggestion: The above equations are valid for the fundamental wave of electrical current and voltage. Nowadays with the nonlinear loads, the above equations may be somewhat off. It is a good idea to check for the voltage and current harmonic content or to simulate the power distribution system by adding nonlinear loads to obtain the harmonic content values.