I have an application were I have a buried air duct that has an intake air temp of 40C and I need to determine the duct length to acheive an air exit temperature of 30C(geothermal application). Based on below, do the calculations look correct?
Paramaters:
Pipe inside dia (ID) = .055m
Buried depth (X) = .76m
Soil temp at depth (Ts) = 295K
K of Soil (Ks) = .5W/m-K
Air inlet temp (Tin) = 313K
Air outlet temp (To) = 303K
Soil surface & air temp (Ts / Ta) = 313K
K of air (Ka)= .027W/m-K
Prandtl No (Pr) = .7
Visc of air (v) = 192e7N-s/m^2
Mass flow rate (Vm) = .013kg/s
Heat flux on the duct calculated by;
q`=ho*dT where dT=Tave_duct-Ts
q'=137W/m^2
Duct length calculated from [ref Incroprera];
L=(Vm*Cp)/(pi*ID*q`)*(Tin-To)
L= 5.6m
Check:
To=Ta-(Ta-Tin)*exp(-(ht*A)/(Vm*Cp))
where; ht is total heat transfer coeff ht=1/(1/hx+1/ho)
hx is the convective heat transfer coeff hx = Nu*(ka/ID); calculated from Re=(4*Vm)/pi*ID*v and Nu=.023*Re^4/5*Pr^n, where n=.3 (soil cooler than air).
ho is the conductive heat trans coeff ho=Ks/X
For above I substituted Tave_duct for Tin. The resultant To is calculated to be 303.3K
Paramaters:
q'=137W/m^2
L= 5.6m
Check: