I have a contactor circuit (basic start stop etc.). An interposing relay is used between the operator controls and the contactor.

My question is when do I need to place 2 contacts of the interposing relay in series when they are being used to trip a conactor? I realize the point is two have each contact open some of the arc... but in this case the contactor only draws a couple amps (of course there is also an inrush).... and the relay contacts are rated for 20A at rated voltage?

Is there a rule of thumb?

Regards,
TULUM
 
Replies continue below

Recommended for you

No. Hardly at the levels you are describing. I assume that you have AC since you mention inrush. If you have DC, it is quite another game.

Gunnar Englund
 
to explain further..

The rule in the office is 125vdc and up use 2 contacts...

My thoughts are if the contacts are rated for the full voltage and full current... why?

Regards,
TULUM
 
So you have DC! Then you have to watch out.

We have talked this over and over again before. Do a search on kick-back, arcing, snubbers, free-wheeing diode etcetera.

In short: DC never goes to zero, so there is no natural arc extinction. Also, an inductive load (like a coil) has a time constant. Trying to reduce current to zero in shorter time induces a kick-back voltage that tries to keep current up (Lenz's Law about action and reaction). Once an arc has established itself it can last forever. It is a question of energy and driving voltage.

As I said, search the fora or google. Or - why not? - have a look in a text-book on electric circuits.

Gunnar Englund
 
Thanks gunnar...

I will hit the books a bit later... just was looking for some practical insight...