My point is that if the component needs to be inspected, checked, tested, or qualified, then it needs to receive the proper inspection, check, test, or qualification, not some guy/gal walking by randomly tapping it with a small brass hammer.
If it needs to be checked, check it properly. If it doesn't need to be checked because the quality control procedures and work processes assure it is done correctly, then stop taking time creating a false sense of security.
The OP states: "The bolts are installed with a DTI to the nut and inspection is both visual for the 'squirt' and with the .005 gauge." This procedure is either valid or the installation procedure needs to be modified if it is not valid. If the concern is that a bolt or connection was missed, then the quality control needs to be examined, or the inspection needs to be 100%, since all connections are life-and-death critical.
I'm on board with the idea that, as a last check, the tap tells you whether something has gone horribly awry. However, the OP's follow-up post says, "No particular pattern i.e., totally random." which indicates to me that it was not a real inspection, but rather a way for the inspector to feel like he was doing something. If, on the other hand, the "random tapping test" method has been qualified for this purpose, and it represents a systematic, accurate inspection, then I suppose it is fine.