psychedomination
- Jan 21, 2016
- 123
Hi there,
I am a recent graduate engineer and am currently working on a basement wall project. The 8" block basement wall is assumed pinned at the top, pinned at the bottom and restrained at the sides. I am trying to find out the flexural reinforcement requirement in the wall.
My main confusion is coming from my local building code. It states for retaining walls (not pinned at top) for an 8’ wall you can use 12” masonry block with T12s @ 8” centers. It then says for foundation walls where it is pinned at the top, you can use 12” block with T12s @ 24” centers.
I did a quick simplified calc for the design bending moment shown in the attached image. Is there something that I am missing in the calculations that would reduce the bending moment even further to match the requirements of the building code? It doesn't seem like changing the block size from 8" to 12" did anything for the bending capacity of the stem? I the assumed steel reinforcement was taking all of the bending.
After I finished the calcs the wall seemed to be ok with 8" block and T16 vertical bars at 16" centers. When I did the same calculations with the 12" block with T12s at 24" centers as shown in the local residential building code, the bending capacity of the wall was inadequate. Assuming no vertical load on these walls.
So not sure what is going on here?
Also one of the existing wall stems in this basement has reinforcement that is inadequate. How can I go about reinforcing the bending capacity of an existing wall stem?
I was thinking to add columns spanning about every meter along the wall to almost act like some sort of ribbing (like how soldier piles are). But not sure if that would be effective unless the spacing was less than a meter since the reinforcement design is done per meter strip?
Apologies for the various questions but knowing the answers would help me tremendously as I continue to work on harder projects. Any guidance would be appreciated.