Pennpiper's suggestion in the original thread on the subject is to use a "long tangent" elbow in this case, which would work just fine. Just fine, that is, if you can GET such an animal from your piping supplier, and can ensure that it will be used in the correct location by whoever is doing the fitting. We tend to purge our pipe specs (and our pipe design software's fitting catalogs) of unusual fittings, as they're always a problem to source when we need them. I'd rather do an extra weld here and there than be waiting 6 weeks for odd components to arrive.
An ordinary long-radius elbow when inserted the proper distance into even 150# SO flanges gives you a very ugly and asymmetrical fillet weld between the hub of the SO and the OD of the elbow. It's a real mess when you go 300# or higher. The problem is even worse on the branch of a tee. You're going to be welding both front and back fillets on the SO, the front fillet is no problem and in category D piping you are permitted to weld only one of the two fillets. The practice of welding only one of the two welds on a SO is prohibited in normal fluid service in B31.3, so it stands to reason that both welds need to be sound and symmetrical when they're required.
We prohibit the practice on code piping purely on the basis that it looks bad, and we always do both welds on a SO, even for category D.
We prohibit the insertion of a fitting directly into a socket-welding flange entirely. In that case, I think there's sufficient justification to call that a bad practice from a strength and durability perspective rather than just on the basis of appearance.
As to whether there's a specific code prohibition against either practice, I've never seen one but that doesn't mean it isn't in there somewhere. I'll leave it to the people who have B31.3 tatooed to the back of their eyelids to answer the real question posed by the OP.