Adding a tidbit of information from our experience.
We found out almost from the beginning using VFD's you didn't want to put more than two on single transformer. We had a serious problem when we converted fan motors on a 7 cell cooling tower to VFD. We wiped out four motors until the problem was diagnosed and resolved. All our VFD's in this service are now on separate feeds. There is also some type of filtering system at substation feeding the cooling towers, Separating the drives was a very expensive problem to correct.. I can only assume that it payed off as there are still VFD drives on the cooling towers.