Scotty,
When our site went through the Arc Flash calculations (just prior to the release of IEEE-1584), we used the Duke equations for calculating incident energy and appropriate PPE levels.
Arcing fault current is calculated as a percentage of the bolted fault current; higher percentage as voltage increases. This arcing current is used with existing coordination settings to determine the actual clearing time of a purely arcing fault.
For plant level distribution voltage, this adds significant time to the flash. This is where I really disagree with the IEEE-1584 method. The incident energy (and associated flash protection boundary) increases in direct relation with time even through one minute if that's what the clearing time comes to.
Looking at the test data used by the IEEE team, all (or most) of their tests cleared between 6 and 30 cycles. There were also very few test data points. The empirical formulae were based off a very small sample size and very fast clearing times. In the real world where clearing times are significantly longer (for arcing fault current), the IEEE results yield unrealistically high incident energies and extreme flash protection boundaries.
I believe that the proper way to protect against arcing faults is to implement one of the newer technologies to detect both elevated current and photo sensing such as ABB's ArcGuard system.
As noble an idea as arc flash protection is, my peers are convinced that it was a special interest by one particular chemical company who also makes the fibers which the PPE is made of, since most of the IEEE team was from that same company.
Sorry for running off on a tangent, but is there anything in particular you want to know Scotty? The general workflow for assessing PPE requirements is the following. Once you see a trend, you can assume a worst-case scenario and base your PPE on that.
1. Have an up to date system model or relaying settings on hand
2. Know the 3-phase bolted fault for each level of the system
3. Use some methodology to determine the arcing fault (IEEE, Duke, etc.)
4. Use the arcing fault current along with other assumptions to determine incident energy and flash protection boundary. These assumptions are such things like space between conductors, distance from point where fault occurs, arc in a box or in the open, etc.
5. Label the equipment
After a while, the trends start to develop. 2500KVA (and larger) transformers with 480V secondaries are hard to protect against as there is a lot of available fault current. These are not your friends when performing an arc flash study. Older plant systems that used a lot of fuses don’t lend well to clearing arcing faults quickly. It’s easy to dictate what must be done to get the incident energy down below a point. It’s much more difficult to find the funding required to make such changes.