ampersand
Structural
- Sep 2, 2005
- 30
Every engineer I know has struggled with determining the design loads for high-seismic anchors, specifically, applying multiple load-increase and strength-reduction factors until the anchorage is ridiculously overdesigned. Plan checkers often don't understand the larger design process, and will require that all of these increase/reductions be applied simultaneously. One very important point to clarify is as follows:
Although the element you are anchoring to concrete (i.e., OMF column) may have been designed for overstrength-level loads (aka omega-naught, or "amplified seismic loads), you are not required to design the anchors for overstrength-level loads. ACI 318 App. D Sec. D.3.2 instructs you to use the load combinations from ACI 318 section 9.2 or C.9.2, which are not the overstrength-level load combinations.
If you choose to design your anchors per App. D Sec. D.3.3.6, you will apply a strength reduction factor of 0.4 to your anchors. The intent of this factor is to ensure ductility. Please note that the intent of the overstrength-level loads, which you may have used to design the element you are anchoring, is also to ensure ductility. To apply these overstrength-level loads to the anchors, and simultaneously use the 0.4 strength reduction factor, is extremely conservative, and is often very difficult to design.
Attached are five pages from ACI 318, with text highlighted, to clearly show what I have tried to explain above. Feel free to keep this document handy in case you need to demonstrate this to a plan checker. I hope this is helpful to some engineers out there.
Cheers!
Although the element you are anchoring to concrete (i.e., OMF column) may have been designed for overstrength-level loads (aka omega-naught, or "amplified seismic loads), you are not required to design the anchors for overstrength-level loads. ACI 318 App. D Sec. D.3.2 instructs you to use the load combinations from ACI 318 section 9.2 or C.9.2, which are not the overstrength-level load combinations.
If you choose to design your anchors per App. D Sec. D.3.3.6, you will apply a strength reduction factor of 0.4 to your anchors. The intent of this factor is to ensure ductility. Please note that the intent of the overstrength-level loads, which you may have used to design the element you are anchoring, is also to ensure ductility. To apply these overstrength-level loads to the anchors, and simultaneously use the 0.4 strength reduction factor, is extremely conservative, and is often very difficult to design.
Attached are five pages from ACI 318, with text highlighted, to clearly show what I have tried to explain above. Feel free to keep this document handy in case you need to demonstrate this to a plan checker. I hope this is helpful to some engineers out there.
Cheers!