Dear fellow engineers,
I am delivering some pumps for the Norwegian Off shore market and my customer have requested a 4H mechanical run test according to API 610. The bearings are a ring oil-design according to the standard.
Now my pump supplier tells me that they will not measure the bearing temperature during the test as they think it's not mandatory.
My understanding of the API 610 is that during shop testing the sump oil temperature rise shall not exceed 40K above the ambient temperature. (Paragraph 6.10.2.4)
We ordered a 4H mechanical run test which is stated under chapter 8.3.4 in the standard. I quote the standard:
8.3.4 Optional tests
8.3.4.1 General
• If specified, the [highlight #FCE94F]shop tests[/highlight] described in 8.3 4.2 through 8.3.4.7 shall be performed. Test details and required data
(such as vibration and temperature data) shall be agreed upon by the purchaser and the vendor prior to
conducting the tests.
8.3.4.2 Mechanical run test
• 8.3.4.2.1 If specified, the pump shall be run on the test stand at the rated flow until oil temperature stabilization
(6.10.2 4) has been achieved.
• 8.3.4.2.2 If specified, the pump shall be mechanically run at the rated now for 4 h
As you can see the test is refered to as a shop test.
For the record, here is paragraph 6.10.2.4 which is a part of the design chapter:
6.10.2.4 Sufficient cooling. including an allowance for fouling, shall be provided to maintain oil and bearing temperatures as follows, based on the specified operating conditions and an ambient temperature of 43 •c
(11 0 "F)
a) for pressurized systems, oil outlet temperature below 70 "C (160 "F) and bearing metal temperatures (if
bearing-temperature sensors are supplied) less than 93 oc (200 •F): during shop testing, and under the most
adverse specified operating conditions, the bearing-oil temperature rise shall not exceed 28 K (50 •R);
A) is not applicable for my pumps.
b) for ring-oiled or splash systems, an oil-sump temperature below 82 •c (180 "F); during shop testing, the
sump oil temperature rise shall not exceed 40 K (70 "R) above the ambient temperature in the test cell
measured at the time of each reading and (if bearing-temperature sensors are supplied) outer ring
temperatures shall not exceed 93 •c (200 "F).
NOTE Pumps equipped with ring-oiled or splash lubrication systems normally do not reach temperature stabilization
during performance tests of short duration and sometimes not even in 4 h tests Temperature-stabilization testing IS addressed
in 8 3 4 2 1
Can someone with the proper experience please tell me who's right and if I am wrong, why?
For the record my company delivers a lot of API 610 pumps and this has never been a issue with any other supplier before.
Thanks for the help!
8.3.4.1 General
(11 0 "F)
in 8 3 4 2 1
