API 5LB for low temperature
obernal
Materials
Jan 24, 2012
4
We have a pipe API 5LB with t= 0.375" that it was used in the relief system, however sometimes the line in very short times working up to 10 minutes will be exposed to temperatures of - 22 ° F. Can This pipe can withstand this temperature. The problem is already is bought the piping.
Regards.
Oscar B.
What is the design construction code? What is the calculated hoop stress at the -22 F temperature?
You also need to consider whether welds can withstand the temperature.
The code is ASME B31.3, we are designing a pipeline of a Plant Storage LPG.
You need to follow the requirements of FIG. 323.2.2A and the permissible temperature reductions as depicted in FIG 323.2.2B based on the stress ratio at the design/operating condition. If you are using Joules-Thompson cooling in your calclation of the low temperature, it is counteracted by decreased pressure. You need to calculate the stress ratio at -22 F.
this requires separate design calculations/ design evaluation per ASME B31.3
I have developed design software and could assist
send me an e-mail with all relevant details if you like