Any one know how to size a vacuum breaker

Status
Not open for further replies.

rahuljha

Chemical
Jun 30, 2007
1
I have been appointed to size a vaccum breaker in slurry pipe line. Does any one have experience in doing this?
 
Replies continue below

Recommended for you

We have atmospheric tanks that will be blanketed with nitrogen, only a few inches water column over pressure. The tanks will have PVRV safety in case the nitrogen generator fails while the tank is pumping out. We could then pull a vacuum, collapse a tank, ETC. The vac relief sizing is based on maximum flow rate out gpm from the pump curve converted to air flow SCFM for sizing the vac relief.

More specifics on your process may help others respond to your question.
 