Hi,
I have to size Anchorage for vertical tank on 4 legs, for which only seismic loads govern ,after calculation per IBC code, the seismic moment is 145 kips ft, and the seismic shear is 8 kips.
As the BC anchors is 96 in, the tank height is 30 ft, and the total tank weight is 160 kips.
conclusion the tank do not require anchors. No tension loads on legs.
And the Shear loads of 8 kips Can be retined Only by friction of 160kips on concrete flor.
So my question . This conclusion is it right?
I am asking This question because some structural engineer said to me that per rule of the thimbs the anchors Shear is about 15 per 100 of the total tank weight
Do you khow This rule and is is correct for This case.
Thanks.
Laurent.