- Unless you are purposely passing your rebar tensions into other reinforcing within the member, I believe that Appendix D style anchorage checks that address concrete breakout are appropriate, whether your bars are developed or not. To my knowledge, you don't need to hook the bars but it certainly wouldn't hurt.
- One popular approach is to use the appendix D
provisions intended for post installed rebar which is not hooked (by definition I suppose). In that case, an additional check would be ensuring that your bars are developed for the force that
you intend to transfer. If you can't achieve the necessary development over your developed length then hooks or end anchors may well help with that.
- HILTI's developed some pretty great software for rebar anchorage of this sort. You might look into the software and the theory behind it:
Link. Europe seems to be taking the lead on this at the moment.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.