“ACI 318: 13.4.2.1 – Openings of any size shall be permitted in the area common to intersecting middle strips, provided total amount of reinforcement required for the panel without the opening is maintained.”
I totally agree with the first part of the sentence. My interpretation about the latter is:
a) The amount of reinforcement equivalent to that interrupted by the opening will be added on the sides of the openings
b) Reinforcing bars affected will be cut right by the opening. The total number (not weight) of reinforcing bars is maintained.
Interpretation a) appears to be more appropriate after reading this sentence for a good few times. But it will be inapplicable for the project I am working on as there will be no room to host the ‘total amount of reinforcement’ within column strips for some big penetrations in the middle.
If interpretation b) is correct, shall slabs by penetrations be treated as free-stand for some oversized holes? And how to quantify the latter?
I wish to thank you all in advance.
I totally agree with the first part of the sentence. My interpretation about the latter is:
a) The amount of reinforcement equivalent to that interrupted by the opening will be added on the sides of the openings
b) Reinforcing bars affected will be cut right by the opening. The total number (not weight) of reinforcing bars is maintained.
Interpretation a) appears to be more appropriate after reading this sentence for a good few times. But it will be inapplicable for the project I am working on as there will be no room to host the ‘total amount of reinforcement’ within column strips for some big penetrations in the middle.
If interpretation b) is correct, shall slabs by penetrations be treated as free-stand for some oversized holes? And how to quantify the latter?
I wish to thank you all in advance.