The long post below here is what I sent ACI on the previous thread. I'm reproducing it here for everyone's enjoyment (place sarcasm icon here).
[blue]My question to ACI was this:
I have been discussing an issue related to ACI 318-05, section 10.5 with a number of other engineers on an engineering forum website. The issue that has many of us confused is as follows:
Section 10.5.1 through 10.5.4 presents minimum areas of reinforcement for flexural members. 10.5.1 provides a formula for As,min for tensile reinforcement.
10.5.2 provides for T-beams with flanges in tension.
10.5.3 provides an out for very large sections, using the 1/3 greater than As(calc).
So all of these are very clear. No problems.
However, we come to 10.5.4 and it states that for "structural slabs and footings of uniform thickness" we are told that As,min is the AMOUNT (commentary) required by 7.12.
The confusion we have here can be resolved into two different interpretations:
Interpretation 1.
For structural slabs and footings - 10.5.4 points you to section 7.12 and you calculate 0.0018bh and insert that into your structural slab or footing in any place within the thickness you wish. 7.12 doesn't require positioning of the min. steel in the tension area. You can put it in the middle, in the top, split it between faces, etc. Also, since 10.5.4 refers to 7.12, we don't need to meet 10.5.1-3 at all for slabs and footings. In addition, the 318-08 commentary for 15.10.4 seems to imply that the 7.12 reinforcing can be place anywhere within the section.
Interpretation 2
Section 10.5.4 is located within section 10.5 which is clearly dealing with flexural reinforcement minimums in tension. Therefore, 10.5.4 is referring to 7.12 to give us an AMOUNT of As,min, and this should be placed in position where tension occurs. It should never be split between faces, placed in the center of the section, or especially placed in the compression area of the section.
In addition, section R15.10.4 states that this 7.12 reinforcement should be placed "as deemed appropriate for specific conditions" - therefore, the only specific condition that would sway me where to place the reinforcement would be where tensile stresses occur.
This section has produced numerous lines of communication on our website and I know it is a very confusing section of 318. I would ask if you could clear this up for us.
1. Does 10.5.4 imply that 7.12 is simply an AMOUNT of reinforcement and that it still should be placed in tension areas?
2. Does 10.5.4 then negate the use of 10.5.1-3 for structural slabs and footings or should structural slabs and footings also meet those sections in addition to 7.12?
3. Should the 10.5.4 reinforcement from 7.12 be a second check on As,min. In other words, do we check 10.5.1-3 for a structural slab and THEN also check to see if it meets 7.12?
Thanks for your help.[/blue]
Here is ACI's response:
[red]ACI publishes codes, specifications, and reports for the concrete user. This message is in response to your technical question/inquiry.
ACI 318 is a consensus document and thus language is debated until all committee members can come to an agreement. This may not lead to the most concise set of requirements as many voices are trying to relay their thoughts.
Question 1. Attached is a copy from MacGregor and Wight book addressing this issue. see the attachment below
Question 2. Section 10.5.4 directly sets the minimum requirement for a subset of flexural members, structural slabs and footings of uniform thickness.
Question 3. See answer to Question 2.
Sincerely,
Technical Staff [/red]
[blue]So it appears that they refer to MacGregor's book and in it he clearly indicates that the 7.12 steel is a tensile reinforcing and should therefore be placed in the tensile area of the footing or slab.
They also indicate that 10.5.4 "directly" specifies the min. steel for slabs and footings in response to my question on whether slabs and footings also need to meet 10.5.1, 10.5.2, etc.[/blue]
(NOTE - the document that ACI sent is attached to this post.)