The equivalent uniform pressure distribution was originally proposed for MSE Walls many years ago since there was not a rigid foundation interface (soil on soil, I think it was attributed to Myerhoff). The resultant location is determined by the eccentricity of the loading on the structure and distributed over the Base - 2*ecc thus a higher uniform pressure.
At some point in recent years, AASHTO adopted this model for all gravity walls except those with a rigid foundation (ie: on rock as you noted). Even worse than that, overturning is not directly checked anymore and only an eccentricity check is required, ecc < B/3 or something like that. Just about the time you have figured that out, add load factors to the calculation and you get an eccentricity value that is pretty close to meaningless and just an empirical value to be measured against another calculated value.
In the older AASHTO ASD criteria, eccentricity criteria was < B/6 and made some sense (eccentricty in middle third of footing thus no negative heel pressure.) Now it is just numbers. Most people still check overturning but you don't have to.
Just a few thought..