70:250.30(A)(1) Exception 2
lyla1711
Hello, forum. I've learned a lot reading here over the years - thanks to all the contributors.
I have a question on grounding and bonding of a customer-owned primary service in the US, falling under the 2017 NEC. It's semantics, but I'm curious to hear how other interpret it.
Article 250.30(A)(1) Exception 2 (along with the 250.30(A)(2) Exception) says that we can omit the SSBJ between the transformer and the first disconnect provided we bond N to G at the transformer and the first disconnect. If the first disconnecting means is located outdoors (pad-mounted transformer five feet off the building feeds over to an exterior switchgear cabinet with a single breaker in close proximity which feeds directly into a building), does 250.30(A)(1) Exception 2 apply?
Here's the verbiage:
(1) System Bonding Jumper. An unspliced system bonding jumper shall comply with 250.28(A) through (D). This connection shall be made at any single point on the separately derived system from the source to the first system disconnecting means or overcurrent device, or it shall be made at the source of a separately derived system that has no disconnecting means or overcurrent devices, in accordance with 250.30(A)(1)(a) or (b). The system bonding jumper shall remain within the enclosure where it originates. If the source is located outside the building or structure supplied, a system bonding jumper shall be installed at the grounding electrode connection in compliance with 250.30(C).
Exception No. 2: If a building or structure is supplied by a feeder from an outdoor separately derived system, a system bonding jumper at both the source and the first disconnecting means shall be permitted if doing so does not establish a parallel path for the grounded conductor. If a grounded conductor is used in this manner, it shall not be smaller than the size specified for the system bonding jumper but shall not be required to be larger than the ungrounded conductor(s). For the purposes of this exception, connection through the earth shall not be considered as providing a parallel path.
(2) Supply-Side Bonding Jumper. If the source of a separately derived system and the first disconnecting means are located in separate enclosures, a supply-side bonding jumper shall be installed with the circuit conductors from the source enclosure to the first disconnecting means. A supply-side bonding jumper shall not be required to be larger than the derived ungrounded conductors. The supply-side bonding jumper shall be permitted to be of nonflexible metal raceway type or of the wire or bus type as follows:
(a) A supply-side bonding jumper of the wire type shall comply with 250.102(C), based on the size of the derived ungrounded conductors.
(b) A supply-side bonding jumper of the bus type shall have a cross-sectional area not smaller than a supply-side bonding jumper of the wire type as determined in 250.102(C).
Exception: A supply-side bonding jumper shall not be required between enclosures for installations made in compliance with 250.30(A)(1), Exception No. 2.
In my opinion, the art.250.30 A(1) System Bonding Jumper requests a single SSBJ at the source enclosure, and Art.250.30 A(1) exception 2, permits 2 SSBJ: one at the source and the second at the disconnector side. In this case, we may not connect these two SSJBs with a bonding wire in order to avoid two grounding paths.
It is not Art 250.30 A.jpgclear how the load side SSJB will be grounded in this case.
A bonding jumper in the service entrance switch?