dvd-
First, I want to let you know that I am no psychrometry expert so take what I have said with a grain of salt. (I used to work for a manufacturer of industrial dryers). As far as I know, most thermoelectrically cooled chilled mirror systems are good to about 85degC. If you need to use this system, you would require a sampling system which would cool the gas stream to a usable temperature, so your dewpoint better be below this value and there had better be pressure compensation if the sample is at some other pressure than that in your oven. As far as radiation being a source of error (as pointed out by Witchdoc) in the gas temperature measurement method I had proposed, it would certainly be necessary to properly shield the temperature sensor from radiation souces (
I don't know how your oven is designed, but normally, the energy source is mounted so as not to directly fire or radiate into the conveyor space. Radiation should not be a big source of error in this case.
In your original post, you asked for ways to to measure "wet-bulb" temperature. If so, your only means of doing this directly that I'm aware of is with a sling type or wetted wick/fan combo. Anything other than this method involves some form of humidity sensor with equations for indirect measurement of wetbulb temperature. Even the EPA method described by Witchdoc does not give wet bulb temperature. You can derive (admittedly accurately) moisture content from this method, but you still need to do a calculation to obtain wet bulb temperature (which is still just that, a calculation potentially riddled with mathematical innaccuracy if not intended for use at these high temperatures). I would suggest a quick phone call to ASHRAE to ask them if they have any literature on high temperature pshychrometry. All I know of is ASHRAE's RP1060. The stated ranges of interest for ASHRAE RP-1060 are:
Temperature: 200-320°C (400-600°F),
Pressure: Low corresponding to altitude of 2250 meters
(7500 feet) to high of 5 MPa, and
Humidity Ratio: 0 to 1 (max.)
There is also a source of work by Hyland & Wexler as well as a practical book entitled "Psychrometrics: Theory & Practice" by Joseph B. Olivieri (Editor), Mildred Geshwiler (Editor), T. Singh (Editor)
Good luck...