Yes, a better UPS specialist. But, hey - aren't we that, too?
Sorry, didn't really mean to be mean.
I did some work in a spread-sheat, which can be found at
I think it is correct. But would appreciate if someone checked the results against known-good data.
Re: starting an induction motor from a VFD. You can start fom zero RPM with even less than rated current. So, I see no reason to make the UPS very large. Then again, some UPSes arent ready to see a VFD input rectifier and its not-so-nive current waveform. So, then you may need a PFC/AFE in the VFD. Which can be a problem to run from an UPS.
I think that you should look very seriously into the flywheel solution.
But, first of all: Please give us (and the specialist you are going to consult with) complete data. The green cells in the spreadsheet say what those data are.
Gunnar Englund
--------------------------------------