We continue to experience higher than acceptable overall vibration levels in large, say 900 to 1250 hp two pole, Babbitt bearing electric motors. The predominant peak vibration energy is usually 3X in either the vertical or axial plane.
Current Example: outboard vertical reading 1.3 ips overall, with 1.06 ips at 3X. 2X is .145 and 1X is .725.
What are some of the most common causes of 3X vibration?