Good Day!
we have an electric motor coupled to a blower for almost 2 months and then the fault happened: burnt terminal wire.
Supply Voltage Measured:230/237/234
Unfortunately we can't measure current.
We tried to jog it but the situation get worst, Line side Line 1 of the main breaker, burnt!
We checked the motor connection and found out that Line 1 and Line3 of the 6 Wire YD connection was interchanged.(diagram attached)
Motor Details:
HP: 10
Phase: 3
Voltage: 220/380/440V (220V YD Connected)
Ampere: 26
RPM: 1800
Hz: 60
Controller: Wye Delta 40A 220V
Why did the motor controller: Breaker, contactor, OL relay and any of the control wire didn't get any damage. Instead the line side of the Main Breaker supplying the controller got burnt.
What do you guys think?