Quick (and probably painfully simple) question:

I have a 3phase, 60Hz, 3HP motor wired up to 460V.

Based on this information alone, is it possible for me to calculate the running aperage? Do I need to assume a power factor to accomplish this? What should that assumption be?
Thanks
 
Use NEC Table 430.250....
3HP Full-Load Current @ 460 Volts = 4.8 Amps

Obviously when running below full load you will be under this value.

If you can get all the information off the nameplate work the following EQ:

Amps=HPx746/VOLTSx%EFFxPFx1.73
or you could estimate efficiency 92% and power factor 80%

This would give you:
Amps=3x746/460x.92x.80x1.73
=3.8

So you would be somewhere between 3.8-4.8 Amps

Obviously the best thing would be to actually take an Ammeter and measure the current.


David Baird

Sr Controls Designer
EET degree.
Journeyman Electrician.
 
Exactly as dbaird said. The line current is given by; Il = HP*746/(1.732*V*EFF*PF)

Yes you need to know or assume the power factor (PF) and efficiency (EFF) too.

For this size motor assuming it is 4 poles I will give ; PF~0.80 and EFF~0.85

Il = 3*746/(1.732*460*0.85*0.8)= 4.13 amperes
 