I have a very strange situation on a cement plant. We have a utility grade billing meter(Enermax)installed. This meter is telling us that the PF is leading at all times. This does not tie up with their electricity account.
We where called in to check with a Power Quality analyzer (Hioki).
The system is 550V 3P. I have attached the vector diagrams of the Enermax and the diagram read directely from the busbar from the Hioki. The Enermax is a 3w meter with the 3 voltages and 2 x currents going into it. The Hioki has all 3 voltages and 3 currents going into it, so it is a true reading, whereas the Enermax is a calculated value.
The kW and kVA readings are almost identical but the Var value is different(Leading on one and lagging on the correct reading).
There are no capacitors in the system anywhere.
The meter manufacturer is adamant that their reading is correct and the motors must be generating vars (All induction pump motors so highly unlikely).
Is there any problem with using 2 wattmeter method when calculating the Vars?
Does anyone have a standard list of expected PF for each phase to get a resultant total PF when using 2 Wattmeter.
I havent used vector diagrams in decades and was also wondering if anyone can help with a expected vector diagram of a 2 wattmeter recording and a full 3phase recording?
Thanks in advance.
I have a very strange situation on a cement plant. We have a utility grade billing meter(Enermax)installed. This meter is telling us that the PF is leading at all times. This does not tie up with their electricity account.
We where called in to check with a Power Quality analyzer (Hioki).
The system is 550V 3P. I have attached the vector diagrams of the Enermax and the diagram read directely from the busbar from the Hioki. The Enermax is a 3w meter with the 3 voltages and 2 x currents going into it. The Hioki has all 3 voltages and 3 currents going into it, so it is a true reading, whereas the Enermax is a calculated value.
The kW and kVA readings are almost identical but the Var value is different(Leading on one and lagging on the correct reading).
There are no capacitors in the system anywhere.
The meter manufacturer is adamant that their reading is correct and the motors must be generating vars (All induction pump motors so highly unlikely).
Is there any problem with using 2 wattmeter method when calculating the Vars?
Does anyone have a standard list of expected PF for each phase to get a resultant total PF when using 2 Wattmeter.
I havent used vector diagrams in decades and was also wondering if anyone can help with a expected vector diagram of a 2 wattmeter recording and a full 3phase recording?
Thanks in advance.