Civiltech Shoring Suite - Determination of slope and moment
LockeBT
Anyone familiar with the Shoring Module and their methodology to come up with the Slope for Soldier Pile? I am checking their output and I want to make sure I can get the same answers myself. However I am running into some trouble coming up with the same slope (and in turn, deflection).
Using the Hinge-Method for soldier pile with multiple braces (per CalTrans) I was able to come up with the same reactions and embedment depth as the program.
For shear, moment, slope and deflection, the program uses the double-integration method (which is the same as finding area under the curves). Shoring Suite Manual Capture.PNG
Since some of the loading gets complicated (such as the Boussinesq loading curve), integrating those equations at multiple segments gets quite hairy so I used the trapezoidal rule with small segments to approximate. Results for shear and moment were very close as you can see.
My trouble is going from the moment curve to the slope. There isn't a location along the depth were I can comfortably predict that the slope would be 0 as my starting point. And no, it isn't at where the moment is max.
This has been bugging the hell outa me. Any help is much appreciated.
Forgive me, as it's been a while since I've done deflection calculations by hand. Could you not do some calculations around the continuity of the slope above and below the upper brace point?
To understand the problem more clearly, could you give all your used inputs, namely lengths between pile reactions, loading, section properties, etc. Knowing all used inputs, gradient and deflection equations can then be derived and boundary conditions applied.
The Hinge Method assumes the top span and the cantilever as its own span, then everything else below is conservatively treated as simply supported spans. As you can see, both the program's and my output of shear and moment reflect that. The slope is only continuous over the 1st brace but not the 2nd brace. Therefore I cannot use the continuity of the slope above and below the lower brace point.
I can give you all that separately. However, how are planning to determine slope and deflection? Double integration? The boundary conditions (or locations that we know a sure value of slope) isn't simple as it is with conventional beams. I do not have any boundary condition that can help me with determining slope as they are not zero at either support. It is zero at some point between the 2nd support and the bottom of embedment depth, but not exactly at the peak moment within that span. Therefore I am stuck at coming up with that "boundary" condition.
I’m interested to see how the shear force and bending moment equations are derived. The approach I’ve used in the past is by strain energy (SE). I’m wondering if the method can be used in this case. Differentiating the SE w.r.t a point load / moment gives you the deflection / rotation at that point. A zero force / moment anywhere along the beam can also be used. Maybe this method can be used?
I referred to the upper brace. Could you not use some condition of slope continuity there?
This is all dependent on the boundary conditions. It's not clearly a pin or fixed at any point. Perhaps the soil is internally modeled as a line spring with the subgrade modulus of elasticity as 36 times the blow count (saw it in a textbook somewhere, maybe it was Bowles). Though that still doesn't get you to a zero point.
The program can calculate it with no braces, so there is some other mechanism at play. I'll post here if I can think through it and figure it out.
Edit: On second thought, the line spring support would totally mess up the moment/shear diagrams. Maybe the zero slope point could be the centroid resultant of passive pressure shear and the lower brace reaction. This would work without the brace because it would just be the centroid of the passive pressure. I couldn't find any reference for this, so maybe you can email Civiltech directly. I emailed them before and they responded. Also, there is some precedent in gravity pile design with lateral force by taking a fixed point 5' below top of good soil or 10' below top of bad soil, which is codified in my area. Maybe look into references for deflections of gravity piles.
Attached is an attempt to model the pile and solving the unknowns by strain energy, and what look to be different (incorrect) boundary conditions. Although the boundary conditions need to change, the example may give you some ideas. I did find the case an interesting one!
Just posting an updated version of the analysis. This version has introduced an additional boundary condition, requiring the beam to have a zero gradient partially through the supporting ground reaction. Again, these boundary conditions are probably not those traditionally used, but it shows how the energy method can be applied. Mathcad solves the set of equations, thereby obtaining all the unknown variables, and plots the graphs very quickly.
The upper brace does have slope continuity there. I have no issue with the upper span (and brace) as I have more boundary conditions to work with. Deflections are 0 at both 1st and 2nd brace. For the bottom span I only know that deflection is 0 at the 2nd brace. Which is why I have trouble with the bottom span
What I did to get close to the answer was NOT starting at 0 deflection at the 2nd brace. I iterated the locations of 0 slope (which is around the point of max moment), then calculate deflections towards the 2nd brace until it zeroes out.
This is dope. That's a method I rarely see or use in SE. Nice stuff man.
On another note, I was able to track down the method they used. It's based on the method outlined in the "Numerical Analysis of Beam and Column Structures" by William G. Godden. The program manual was a bit misleading
