Odd Vertical Bracing 3
Nick6781
CA
The vertical bracing layout should follow the configuration shown in the snippet below. Since the compression force is continuous through the bracing members, gusset plates, and beam webs, I believe I need to verify whether the weak-axis stiffness of the beam is sufficient to brace the bracing member per Appendix 6. I'll also need to check beam shear.
Am I missing any other critical checks?
Thanks for the elaboration CDLD. I agree that for most beams mode 2 would be more critical though I can imagine a torsion ally strong memento like a HSS, mode 1 could dominate.
Regarding your calculations, it is late in the evening for me so I won't attempt to digest them. Maybe they cover it all, but they seem a little too brief. Though I would suggest that I feel like things are a little more involved than a mere torsional stiffness check. In the same way that LTB quickly gets murky in practice and the analysis is half empirical, this would be similar. Non linear effects would be significant as would incidental eccentricities.
Yeah you may be right.
As for the calculations being brief, I left a lot of them out and mostly just outlined the steps.
For example, calculating the largest unbraced length of the brace and web/stiffener assembly.
I checked the torsional stiffness by analyzing the flanges independently (a simplification), which could alternatively be done by checking the rotation from torsion.
Also, I left out the strength calculations, which also need to be checked for both modes.
In addition to what everyone else said, if the diagonal braces (and brace forces) are large compared to the floor beams, you might want to consider configuring the (large) diagonal brace as a single long member, and interrupting the (relatively wimpy) floor beams between the brace. For example, if your braces are W14x120’s and your beams are W16x26’s I would make the W14 diagonal brace a single continuous member and interrupt the W16’s at each floor to frame to diagonal W14. (This configuration usually simplifies the brace-to-beam connections, and eliminates expensive stiffeners at the brace-to-floor-beam connections.)
Nice discussions.
Question for CDLD, did you use TL/2GJ to calculate the rotational angle theta? Also, I think I'll need to ask for double angles for the beam's ends to increase the torsional stiffness of the connections.
You can apply fictional loads in opposite directions to the flanges of the bracing beam (in other words torsion) and calculate the amount of beam rotation.
With the beam rotation you can determine how much the top and bottom flanges translate laterally, in other words the stiffness.
I didn't calculate the rotation angle theta.
I calculated the lateral deflection of the flange by using a 1 kip load and moment of Inertia equal to Iy/2 (moment of inertia of the flange).
In fact, I didn't calculate anything, these were arbitrary numbers to illustrate the steps.
If you want to go the more detailed route and calculate the rotation angle, you can refer to AISC DG 9.
I believe you will get slightly better stiffness values this way.
Not sure off hand if that formula is correct or not.
There is a spreadsheet on Steel Tools, called Torsional Analysis of Steel Members, which will provide the calculations for you.
I'm not entirely sure if that approach is valid, but I also couldn't find anything in the code that addresses Mode 2 directly.
We all seem to be in agreement regarding your mode 1 so I'll leave that be. As @CDLD intimated, mode 1 resistance probably needs to be a pre-condition of the other modes further down the hierarchy of instability.
Regarding mode 2, I see that as being one or the other of these (or a combination of both if one wants to get that fancy):
1) The diagonal braces doing the torsional bracing of the beam as roll beams.
2) The beam torsional capacity being the thing that braces the beam torsionally.
I think that one could boil this down reasonably to a rigid bar & spring check that is common in the first few chapters of many texts on stability. My quick and dirty (and probably incorrect) on this is shown below. Given the situation, I would of course add some fat to that somehow.
Obviously, "rigid bar" should be setting of all manner of alarm bells to the tune of "maybe a stiffener here".
Nick another option you have is to rotate the W strut 90 degrees.
- This provides ample stiffness for mode 1
- No need to check mode 2
As for as a WWKKD solution, I would probably do this:
1) Assume that the diagonals are doing 100% of the job of rotationally bracing the beam.
2) Conservatively check the diagonals for the bracing function by just doing a K=1.0-ish buckling check on the braces for the axial load in them and a faux unbraced length that extends the brace length to the center of the beam depth.
Yeah, the connection flexibility enters into it to some degree.
Ok.... So I though I'd do post some pretty pictures based on a real work example.
Here is the example:
Circled yellow is the connection with a single web stiffener behind.
Circle orange is the single framing member.
And here are the buckling modes modelled. Note the single framing member has been removed for for this modelling. Load is 210kN from a 5m wide, 30m stair and equipment tower. Modelled using perfect pins at all constraints.
Mode 1: Eigen Value: 4.5
Mode 2: Eigen Value: 5.13
Mode 3: Eigen Value: 5.13 (Picture not show, largely just variations on the same theme)
Mode 4: Eigen Value: 5.98 (Picture not show, largely just variations on the same theme)
And if you add that single framing member back into the analysis with a lateral restraint you get the previous 'Mode 2' becoming the dominant Mode 1 with an Eigen Value of 5.16
Thanks! This is very helpful.
What software is this? For buckling analysis, is the eigenvalue essentially the critical load factor (or a kind of safety factor)? In other words, for the system to fail in Mode 1, the load would need to be 5.16 times the applied axial load—correct?
Yes that is correct the eigen value is essentially the critical load factor, in fact this is where the concept of at least the initial theoretical concept of a critical load factor comes from as I understand it. This was done via non-linear buckling analysis analysis which means that the stiffness matrix used to calculate the eigenvalue is not the initial linear stiffness matrix but incorporates non-linear effects.
Of course, as you likely know, the buckling critical load factor is an calculated theoretical value. In the real world imperfections can play a big hand in reducing the actual buckling load. In this case I would regard anything above a eigen value of 4 to be just satisfactory. Anything under starts to get into starting to territory of needing to dig deeper. But it depends heavily on what assumptions are used and the sensitivity of the buckling to to imperfections. Experience in suitable modelling and comparisons to actual testing or empirical formula based of testing is important to safely interpret the results.
In some designs I've spent extensive time calibrating my FEA models against the theoretical/empirical formula. That way when I have shapes and configurations with local differences I can readily check the effect of the local differences on the more global behaviour.
The software is Nastran-InCaD which is in Autodesk Inventor. There are many FEA software with similar capabilities. This is the one I have access to and use.
IDEAStatica is one of the best connection FEA software out there. It also does some of the best jobs of explaining how to interpret buckling analysis. Have a look at these links:
