REQUIREMENT OF COOLING TOWER IN WATER COOLED CHILLER SYSTEM
123131415
IN
Dear member,
I am working with Petro -chemical plant wherein central colling tower is available for entire plant (process and non -process building). We are purposing water cooled screw chiller based on total thermal load of building for comfort air conditioning for non- process building (i.e. control room, fire control room, central canteen etc ). chilled water supply and return is 44 and 55 deg-F.
Water from central cooling tower is available at supply Pressure of (Min/Normal/Max/Design : 54 / 57 / 64 / 114) in psi and Return pressure of (Min/Normal/Max/Design : 31.5 / 34 / 40 / 114 ) in psi
Supply temperature in Deg-F ( Min/Normal/Design : 82.4 / 91.4 / 149) Return temperature (Max/ Design : 113 / 149 ) at battery limit of each building.
my question is we required separate cooling tower for heat rejection or water from central cooling tower is adequate for heat rejection based on above utility data.
Thank you
What you need to know is flow....
Basically what's the heat rejection / flowrate capacity of the cooling tower versus the duty that everyone else uses.
Ditto flow to everyone else. Wha tis available now won't be the same when you add in another user unless you're only adding 10-20% to the flow
water cooled Screw Chiller of 2nos x 125 TR + 1standby proposed @ chilled water supply/return 44 / 55 deg-F. Heat rejection of cooling tower 312.5 TR considering 25% for compression. Wet bulb temperature for site is 81.5 deg.F . my question is utility condition at battery limit will eliminate the need of separate cooling tower or we required separate cooling tower for heat rejection.
How many TR of heating is the cooling tower operating with now?
You're giving us little snippets of information here, not the whole picture.
For yourself and others draw out a schematic diagram / PFD of the existing cooling water system and we may be able to help you, but there's about 5% of the required information here at the moment.
If you don't shut down on high pressure your cooling capacity will be pretty small when the cooling water temperature is 149F. Is that ok?
Does the central cooling tower really have 312 tons of spare capacity just hanging out waiting for your building?
I can't guess what "battery limit of each building" might mean
Shared Central Cooling Tower Usage:
Applicable if the central cooling tower has sufficient margin (recommended additional load ≤ 20% of design capacity) and water quality complies with the ISO 14644-1 cleanliness standard.
Independent Cooling Tower Scenarios:
Critical facilities such as control rooms/fire control centers (requiring 100% reliability).
Central cooling tower design margin <10% or water quality reports indicating suspended solids >50 ppm.
If additional cooling towers are needed, I can assist.
The process equipment with in a chemical plant are more tolerant to temperature changes outside of the design limits though heat transfer efficiencies might suffer.
You need to be mindful of the fact HVAC chillers are lot more sensitive to cooling water temperature ranges as well as the quality of the cooling water in comparison to process plant equipment. An out of range temperature can cause the chiller to shut down on safety controls.
