Using a backpressure regulator to maintain a minimum pressure
jwpyr8
3
I'm designing a pumping system where I have a large variance in flow and the starting Elevaiton is higher than my end elevation. So at low flow, I would not stay on the pump curve. However, at the peak flow, I am on the curve due to line losses. I'm considering installing a backpressure valve on the line to maintain a minimum pressure in the line so the pump is always on the curve. Does this backpressure valve act as a static pressure loss that is always present in the line? As an example:
Lets say my pump needs to have at least 10 psi of backpressure to stay on the curve at a good spot. So I set my backpressure regulator at 10 psi. During peak flow, my line loss (assume 12 psi) downstream of the backpressure will exceed my backpressure regulator setpoint. Ignoring elevation head, would my pump see a velocity head loss of 22 psi?
Thanks in advance.
The valve will have a head loss as flow passes through it according to the valve's Cv at the time. The loss will be constant, if the flow, upstream and downstream pressures remain constant. Of course, if you open or lose the valve a bit, then Cv changes, then flow changes and the system must reach a new pressure equilibrium with that new flow passing through the valve.
It's not clear how you intend to use the valve. Your symbol indicates a downstream pressure controller.
If you set your valve to give a constant pressure drop of 10psi at all flow rates, then the pump will see an initial resisting pressure of 10psi, because at no flow, you will not yet have a 12psi pressure loss in your downstream pipe length. As flow increases in the pipe, pipe pressure loss will rise and the pump will see a total resistance of 10psi + whatever the pressure loss of the pipe is at the current flow rate.
In any case, no matter how the valve is controlled, the pump will see a resistance of the sum of the valve loss + line loss at any given flow rate.
What is the purpose of this?
Why not just let gravity do the work?
If you need variable flow rates use a vfd.
So far this sounds like a really bad idea and not fully developed or understood
My understanding of how a backpressure regulator works is that you set it for a given pressure to be maintained on the upstream side. So if you set it for 10 psig it will try to maintain this pressure on the upstream side. If the pressure downstream is lower than 10 psi say 5 psi at a given flow, it will close just enough to produce a pressure differential of 5 psi so that the gauge pressure on the upstream side is the set pressure 10 psig. If the pressure rises on the upstream side (due to upstream head increasing or downstream friction loss increasing) then the valve will open more to reduce the pressure loss through the valve to maintain 10 psig on the inlet. If the pressure keeps rising above 10 psig the valve will go wide open which at that point the only pressure drop through the valve is based on the wide open Cv.
The system you have is confusing. If you have a constant speed centrifugal pump, it will be pumping on a given pump curve. You cannot control the flow. At a low flowrate it will produce a higher discharge pressure and at a higher flow it will produce a lower discharge pressure. The flow would be controlled by the system say if you have users downstream that open or close more valves creating more or less of a demand. If this is the case the pump will automatically adjust to produce the flow at a given discharge pressure. With such a system the pump will run out towards the end of curve (low pressure at high flow) as the flow increases not decreases.
Please explain how your system operates in more detail.
I'm with snickster here.
It's not clear what is controlling flow?
But if the inlet side of your back pressure valve goes above 10psi it will just go full open and then you have the pressure drop across a fully open valve to deal with
How are you creating the low flow? Is it by throttling some downstream valve(s)? If so, at the upstream of those valves, high pump pressure at low flow will automatically exist. The shortfall in piping losses will be taken care of by valve throttling the flow and the system will remain on pump curve.
The concept is not clear. Please give complete flow diagram.
For a pump to "stay at a good operating point", it must be operating at constant differential pressure. This then gives you constant flow. Presume this is what you are aiming for ?
Given that you have a varying level in the source tank, the simplest way to enable constant diff pressure is to measure dP across the pump, and use the dp to operate a dPIC loop, which will modulate a dPCV on the pump exit. Dial up the required dP as setpoint at this dPIC. If you have trouble picturing this, talk to your process controls engineer - its a relatively simple loop to configure.
A better description is needed.
Why not considering a VFD to modulate the rotation speed of the pump to acknowledge the flow rate variations +LIC?
LSL and LSH are needed to protect the pump from cavitation and cut the feed to the source tank to avoid overflow.
In any case back pressure valve will not help (review its principle)
Pierre
The OP is not giving more data readily.
In the meanwhile I have analysed the system considering both +ve static head and -ve static head (assisting the pump).
The assumptions in the following curves are as follows:
Pump rated point 10 m3/h, 7 mwc
Maximum piping friction drop 10 psi (approx 7 mwc)
Level difference between supply and discharge tank: 5 max, -5 min.
Pump curve is approximate.
We see that under the assumed conditions we require a CV with 5 mwc pressure drop at 10 m3/h flow to prevent a runaway flow.
Also the CV should be controlled from the differential level between supply tank and discharge tank. It should progressively open when the differential level increases from -5 to +5.
It is possible that under positive static head condition the flow will be less than 10 m3/h.
Sorry it was the weekend and I didn't have time to reply. Thank you for the input. I will try and clarify the system. I will try to bullet point the main points.
- I can gravity flow, but do not want to due to the length of the pipeline and the source of the water. This is wastewater containing secondary solids from an aearation basin going to a DAF. The distance is around 500 ft. I'm worried about air locking and gas locking from nitrification if the wastewater sits in the pipe due a shutdown. It is just easier to pump.
- I am going to use a VFD. The problem is I have a large flow variation. Peak flow is 420 gpm and avg flow is 240 gpm. the pump runs off the curve at the low flow because it is sized for the peak flow and I don't want to size the pipeline smaller than 4". I thought I could potentially use a backpressure valve to maintain a minimum head on the pump to keep it on the curve. I could achieve the same thing by just having a valve I throttle to a maintain a headloss across.
- Flow is controlled using the pump VFD and a FM.
I hope this clarifies.
Thanks in advance.
Keep it simple. The backpressure set point of 10 psi will not have enough energy to provide for the friction loss of 12 psi in the downstream piping. In this situation, there will be no flow at the receiving tank. To get the flow, either increase the set point or reduce the piping length. By sensing your problem, it looks like the pump may not be correctly selected. If the flow drops down the "minimum stable flow", it's not the correct pump. the backpressure set point should be atleast 15 psi to get flow at the exit.
As other colleagues pointed out, the function of the back pressure valve is to keep the upstream pressure constant at 10 psi by constant opening/closing the valve. This will also include the elevation pressure.
You can apply Bernoulli's equation at the valve and the exit.
Consider use of positive displacement pumps attached. I believe that they are basically same application.
  • 11385_Positive_Displacement_Rotary_Lobe_Pumps_20151218_IFC_R0.pdf
Using centrifugal pump I believe you can use a backpressure regulator placed at the very end of the line and set as low as necessary to get enough backpressure to keep it on the curve at lower flows say 2 to 4 psig. This will then add to the 12 psi friction loss at the higher flow.
I guess, OP has more issues with the flow range that goes outside the operating envelope of a constant speed drive pump than the back pressure control and he is finding a solution with a VFD to cover the wide flow range (specially on the lower side).
This post is going nowhere; the OP is not providing data about the fluid, the solid content, the size of the tanks,etc.
Will it be possible to use the source tank as a modulating tank, do you consider agitation on the tank to cope with solid?
Can you operate the pump batch mode?
If no agitation, how do you manage the risk of sedimentation?
You mention peak flow; this is meaningless without info about duration.
What about pipes size and other equipment size (pump, filters if any, valves)?
Please provide a clear scope with real input from you before we are giving up!
Pierre
Sorry for the confusion. What Pierreick is asking is really outside the scope of my original question. I really just wanted to know how a backpressure valve affects the TDH required of the pump to operate on its curve. Because due to the elevation difference, at average flow my pump is not needed and has negative head. So I wanted to know how adding a backpressure valve to maintain a minimum pressure upstream of the line will affect my head requirements at full flow when I do have enough head loss in my system to require a pump. Is the backpressure sustaining valve additive to the friction head loss in the line. My original question was:
I'm not asking for a design of the system.
Sorry if this got blown out of proportion.
The backpressure valve will vary the pressure loss across the valve such that the upstream pressure is maintained at the set point. If you set for 10 psig and the pressure loss downstream is only 5 psi then it will close just enough to produce 5 psi pressure loss so to maintain the 10 psig set pressure. So if the pressure loss downstream decreases from 5 psi then in will close more to produce more pressure loss and if the pressure downstream increases it will open more to produce less pressure drop while maintaining the upstream pressure at 10 psig. If the pressure downstream keeps increasing up to the 10 psig set point then the valve does not have to produce any head loss anymore in order for 10 psig to be maintained upstream so it will go wide open. If the pressure keeps increasing downstream it will stay wide open and the pressure upstream will then equal the pressure due to friction loss downstream plus the pressure loss across the wide open valve.
It just seems overly complicated for a simple problem. If you could explain the design requirements and reasoning maybe a real solution could be provided. Anytime anyone add things to a pump system like this is asking for issues, use the KISS system. I had a guy once had a prv then wanted to install a pressure pump system, rather than installing a bypass on the prv for higher pressure.
