Gunnar:
I used to work a lot on pantographs - more on haul trucks than on trains - but the same should apply. In the summer-months we operate during quite high temperatures (ambient more than 40˚C easily during the day) but heat-wise we did not really had problems. I would have looked into two...
Scott: Thanks a lot for your answer. From a field perspective I thought I knew enough, I've tested a lot of CT in my career and I've used a lot of CT information to determine settings for protective schemes (for instance REF-protection when mentioning Class X CTs) - but never really thought...
Hi
After a discussion I've realized I had a lack of knowledge on CTs - any specifically on specifying the magnetizing current of a Class PTX (X) CT, thus an CT been used in the IEC-world.
In a class X CT the performance is defined in terms of a knee-point voltage and the magnetizing current at...
Thanks for the responses, David and Zogzog:
To answer your question Zogzog:
Voltage up to 66kV present in the yard, although only up to 11kV present inside the buildings.
No exposed live parts in the buildings, and outside all exposed live parts are out of reach.
Thanks
Regards
Ralph...
It is my responsibility to declare people authorized to do work in substations on our mine. Normally it is not a problem, the persons working in the substations is qualified electrical artisans, they do get some training on the safety, the relevant procedures, the operating principles, the...
I am not really familiar with generators or with generator-grounding, but I suppose it might use the same guidelines as applying a zig-zag transformer to a Power transformer.
The first step is to decide how much ground fault current you want to allow.
If you plan to solidy ground the...
gbk: Thanks for the correction.
The first setting is indeed not for inrush but for the magnetizing or energizing current.
Regards
Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon
Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376
The bias setting is used to ensure stability during external faults/conditions while the relay is still sensitive for internal faults.
Settings depends on:
Type of relay, (electromechanical, static, electronic etc) If a Tapchanger is present or not. (especially for an on-load tapchanger)
Type...
Hi
Do you want to change an ungrounded system into a grounded system?
Regards
Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon
Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376
Yes, yes, you are quite right - if there is a element on each phase. Although I can't see any real advantages in doing it on such a way.
Regards
Ralph
Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon
Make the best use of Eng-Tips.com
Read the Site Policies at...
That would be the first time I've even heard about a bus zone scheme connected like that. You sure the reversed CTs were not incorrectly marked? Can't see how such a scheme will stay stable, especially when loaded.
Regards
Ralph
Failure seldom stops us, it is the fear for failure that stops us...
Do a search for SWER (single wire earth return) on this site or on Google.
Also check http://www.ruralpower.org/
I mention SWER specific because it is used (many parts of the world) in rural areas with a low population and density. Some advantages and disadvantages of SWER-systems:
Advantages...
Slavag:
In the new SEL-relays we are using, directionality is an option, but we do not use it. The cables always stay the same length - 1000m - a cable-reel is installed on each machine for propel (travel) issues.
Regards
Ralph
Failure seldom stops us, it is the fear for failure that stops...
I also prefer Marmite's method.
http://tinypic.com/view.php?pic=4vn0som
A picture taken of a damaged 630mm² singe-core cable due to circulating currents. The cable was installed and grounded at both ends, no-one considered circulating currents, and it was probably energized for two weeks...