duh
Electrical
- Sep 23, 2004
- 9
Hey all,
Had a question regarding concentric grounding terminations. We have a 138 - 25 kV delta-Yg power transformer feeding 25 kV switchgear via 3 circuits of 25 kV - 750 kcmil triplexed cable with concentric neutrals on each phase. Our standard is to have the concentric neutral tied to the power transformer (at X0 which is tied to the ground grid), and leave it disconnected at the switchgear end. This would prevent circulating currents through the concentric neutral. However, I was thinking that any unbalanced current would instead flow through the ground grid to return to the transformer, which doesn't really make sense to me. I am curious to know what others are doing in this type of installation (tying the concentric neutral at the switchgear end or not). Why is one better than the other?
Thx,
Pete
Had a question regarding concentric grounding terminations. We have a 138 - 25 kV delta-Yg power transformer feeding 25 kV switchgear via 3 circuits of 25 kV - 750 kcmil triplexed cable with concentric neutrals on each phase. Our standard is to have the concentric neutral tied to the power transformer (at X0 which is tied to the ground grid), and leave it disconnected at the switchgear end. This would prevent circulating currents through the concentric neutral. However, I was thinking that any unbalanced current would instead flow through the ground grid to return to the transformer, which doesn't really make sense to me. I am curious to know what others are doing in this type of installation (tying the concentric neutral at the switchgear end or not). Why is one better than the other?
Thx,
Pete