Hi.
Punglu, I hope you ask about digital/numerical xfr protection.
Ralph and Gbk are right.
I would like add my practical excpirience.
Put your first setting always on the max value, it's depend
on the protection type, for example 50% ( upper level of slope) and 2d harmonic blocking on the minimum value, for example 10%. Put this, provide stability test, connect trafo, provide on-load test and never don't change this first setting. Maybe add cross-blocking option ( it's big Q, we need this option or not).
I know, what will reaction!!! but it's my opinion ( I'm not say, that I'm right), we put in services lot of xfr's with this setting, at size from 15MVA up to 650MVA, it's work and work correct ( was several unwanted trips, was CT problems).
Please pay attention, I told about phase diff protection, not about REF.
New options , as TCH position, very sensitive slope,etc., I don't know, we need it or not.
Regards.
Slava