Need help with home generator

Need help with home generator

Need help with home generator

(OP)
Hello.
I understand this is a forum for professionals, but I have been going in circles trying to find an appropriate home emergency AC generator to power an air conditioner for my elderly parents.
They live in So Cal. and extended blackouts are expected this summer.
The problem: I purchased a 3000 watt Coleman generator (3600 surge) to run a 10 amp, 120 volt air conditioner. When I tried to run the air conditioner, the compressor would not start.

(The name plate on the AC says it requires a 15 amp breaker)

When I called Coleman they said I need at least a 5000 watt, and probably a 7000 watt just to start it. Also, they said I cannot draw the full/max rated currant from one receptacle on the generator.(part of the problem ?)

I would like them to be able to run the air conditioner, but I don't want to buy a 7000 watt industrial generator just to run a 1250 watt AC.
Any suggestions would be greatly appreciated as I have not been able to get any help from electricians, generator sales or manufacturers.
Thank you.
Replies continue below

Recommended for you

RE: Need help with home generator

Sounds like Coleman gave you good advice.
Your generator is probably 120/240 V, which means it can supply 3000 W to a 240 V load, or 1500 W to each of two 120 V loads. The 10 A figure probably refers to full load current. Motors draw significantly more during starting (NEC says a 115V 9.8 A full load single phase motor draws 58.8 A while starting)  This current doesn't last long enough to trip the 15A breaker, but does cause problems for a generator.

Another option might be to rewire and/or replace your motor for 240 V operation.

RE: Need help with home generator

(OP)
Thanks for your reply.

RE: Need help with home generator

Suggestion:  It is good idea to shop around and mention your load. There are other generator manufacturers, e.g. Basler/Kato, etc. If a generator is designed for the motor load, it may have a flywheel, the protective device (a time delay fuse 1.75 x Full Load Current) is also designed for the motor load and one does not have to have an excessive surplus of Watts. A solution might be either to trade it for the larger one, or add a flywheel, or try a soft start of the compressor motor over a soft motor starter.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close