Field welding vs bolting to existing steel structures
Field welding vs bolting to existing steel structures
(OP)
Hello Fellow engineers, I need your help with this one
My client wants to install new equipment to the roof of a building (Equipement will be attached to existing steel beams)
For this to happen, the existing beams needs to be reinforced beforehand.
My only two options are : bolting or welding a new a plate to the existing beam to increase its capacity.
After some research (googling), here is what I learned about the difference between the two options.
Welding :
My problem is that I still don't know which option is the best? what do you think?
Thank you in advance.
My client wants to install new equipment to the roof of a building (Equipement will be attached to existing steel beams)
For this to happen, the existing beams needs to be reinforced beforehand.
My only two options are : bolting or welding a new a plate to the existing beam to increase its capacity.
After some research (googling), here is what I learned about the difference between the two options.
Welding :
- The building is very old and I am not even sure if the steel is weldable (investigation/destructive testing required?)
- Welding requires prepping, cleaning and removing paint from the existing beams (maybe expensive)
- The beam is already stressed (under dead and live load), welding may decrease the capacity of the beam temporarily (because of the heat) and shoring is rerquired
- The beam is on the roof, I do not know if it's feasable to weld.
- May increase local stress and might also require shoring (I am not sure how to quantify the stress).
- Possibly decreases existing beam capacity?
- To me it seems easier than welding and also less expensive ( I am not sure, I have 0 experience in the field)
My problem is that I still don't know which option is the best? what do you think?
Thank you in advance.
RE: Field welding vs bolting to existing steel structures
Make the plate wider than the bottom flange so that the welds are downhand (versus the much harder overhead welds). Your welder will thank you.
If there is sufficient headroom, consider using an HSS (wider than the bottom flange) instead of a plate. You’ll get more added flexural strength per pound of steel with an HSS, and HSS’s are available in longer lengths than plates (eliminating the need to splice multiple sections of plate together.
Reasons to avoid using bolts: Precise field drilling of bolt holes will be required. Field welding splices between multiple sections of plate will still be required depending on how long your beam is.
But of course you still need to determine the weldability of the existing beam.
RE: Field welding vs bolting to existing steel structures
I'll disagree with cliff234 on one thing, though. Drilling the holes is not that difficult if the cover plate is simply clamped onto beam and the holes in the beam flange are drilled through the holes in the cover plate. This is fairly common for bridge girder retrofits.
RE: Field welding vs bolting to existing steel structures
You surely have several other options. One way is to use two bolted channels sistered to the existing beam. The approach of sistering isn't the most efficient from an engineering perspective. But it is quick, easy and practical. You have the ease and simplicity of bolting without having the challenges of potentially requiring slip critical bolting. With the right channels you can potentially double the capacity of the beam. (depending on the beam and the type of channels available)
RE: Field welding vs bolting to existing steel structures
RE: Field welding vs bolting to existing steel structures
RE: Field welding vs bolting to existing steel structures
RE: Field welding vs bolting to existing steel structures
RE: Field welding vs bolting to existing steel structures
RE: Field welding vs bolting to existing steel structures
RE: Field welding vs bolting to existing steel structures
We selected sizes that gave us 7/16" of steel on each side.
Easy to weld an added a lot of stiffness.
= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, consulting work welcomed
RE: Field welding vs bolting to existing steel structures
On a previous project, welded connections caused major problems because of this. We got very far into the process, and some connections were already welded in place. THEN, someone upstream realized the steel is a few decades old and had uncertain material properties. They started naming the requirements that would let them sleep at night. It took quite a bit of work and money to fix that.
Going forward, the only way I would weld to existing is if it's shown on the EOR's drawings and clear enough that it's on them if someone changes their mind later. Bolted is the default at this point.
RE: Field welding vs bolting to existing steel structures
RE: Field welding vs bolting to existing steel structures
It depends on how big of a plate is added, and whether the design is limited by bending capacity or deflection.
I just checked a plate girder I had the section properties handy for. Doubling the bottom flange thickness only increased the top flange section modulus by about 10%, but it increased the moment of inertia by 34%.
RE: Field welding vs bolting to existing steel structures
RE: Field welding vs bolting to existing steel structures
RE: Field welding vs bolting to existing steel structures
RE: Field welding vs bolting to existing steel structures
Friction bolts are not necessary. You are only transfering shear. The biggest differential deflection between the beams is the hole clearance so you are guaranteed to engage the channels unless deflection is tiny. You have deflection compatibility.
While I'm replying I will note that a_urbs's comment about stopping and starting the channel where connections are framed into the beam is highly problematic and cannot readily be addressed by using a bolted plate underneath. You have all sorts of stress flow issues.
EDIT: hokkien beat me to it, I started my reply an hour earlier! As hokie says the channel doesn't need to be full length but I would point out that it does need to be continuous.
So it might be not a good solution if there are intersecting members as has already been pointed out.
RE: Field welding vs bolting to existing steel structures