Rebar 90 degrees hook length
Rebar 90 degrees hook length
(OP)
Question:
Why do some engineers use significantly longer 90 degrees hook lengths than is required by ACI code? For example, having the leg be 24" long for #5 bar, when only 10" is needed.
Background:
Per ACI 318-14,
So #5 needs 10". This is also shown in CRSI manual. However, I've seen two different firms use 24" for both #4 and #5. It seems excessive. I think there must be a reason for it, like it's easier to cut or something. Or maybe it's a regional thing, where "my grandfather did it this way for 1000 years" so everyone does it. I'm in the east coast.
Why do some engineers use significantly longer 90 degrees hook lengths than is required by ACI code? For example, having the leg be 24" long for #5 bar, when only 10" is needed.
Background:
Per ACI 318-14,
So #5 needs 10". This is also shown in CRSI manual. However, I've seen two different firms use 24" for both #4 and #5. It seems excessive. I think there must be a reason for it, like it's easier to cut or something. Or maybe it's a regional thing, where "my grandfather did it this way for 1000 years" so everyone does it. I'm in the east coast.
RE: Rebar 90 degrees hook length
RE: Rebar 90 degrees hook length
Some detailing conditions you are trying to pass the tension around the joint rather than just develop the bar so need the Lext dimension to lap with the bars you are passing the tension to.
RE: Rebar 90 degrees hook length
RE: Rebar 90 degrees hook length
RE: Rebar 90 degrees hook length
RE: Rebar 90 degrees hook length
Post examples of what you’re talking about so we’re all on the same page.
RE: Rebar 90 degrees hook length
@gte447f I get what you mean, using the non-Ldh part of the hook as reinforcement. Similar to what Celt83 said.
@Celt83 You mean as a moment connection, like passing the tension into the perpendicular direction as a moment couple?
@Brad805 I'm suspecting it's something like that. Maybe it's just easy and brainless to cut a piece of rebar to 2'x2' or something.
@BridgeSmith I see, so you'd be double counting the hook for development and for actual tension reinforcement.
@skeletron I don't really do that for footings. I mean bending the bottom bar up into a column or wall. I'd rather add a dowel because I'm more used to it, I guess. But either way works.
RE: Rebar 90 degrees hook length
RE: Rebar 90 degrees hook length
Which is obviously not correct and I see it being abused all the time in situations where there is not enough room to get a bar to develop, so people will just keep extending the tail of the bar until they get enough overall length.
Unless you are providing a larger-than-normal bend diameter (>10*db if I remember correctly), the reinforcement can't be considered to continue developing along the tail of the bar.
RE: Rebar 90 degrees hook length
Putting a critical engineering hat on, do we think that the stiffer load path for development is going to be the inside of the hook, or the long ass tail that someone stuck on it?
Obviously it's going to be the hook so the peak load will be inside the hook
If Ldh isn't provided then you risk breaking the concrete IMO
This is relevant to the detail you provided - the bar from the wall to slab is way underdeveloped inside the slab as the hook is so close to the bottom
The advantage of the longer tail is realised at that at least there is something still anchored into the concrete if a cone blows out
But then you have some sort of bar in bending-catenary situation going on, so it's not a primary situation
To me, the advantage of using a hooked bar with long legs is all about construction
I commonly do it for retaining walls - it saves them a bunch of steel and makes it way easier to support all the bars
The horizontal legs support the vertical legs and vise versa, whereas using straight footing bars tied to a short-hooked vertical starter is a floppy system with way more tying required
RE: Rebar 90 degrees hook length
Agreed, that's one of the issues with the detail that I'm working with the original engineer to fix. I'm hired to do quality control and calculations.
That's actually a good argument for doing the longer tail. I can buy that. I don't remember the actual name, but I read a forensic engineering report where a parking garage had a pancaking collapse due to punching shear failure. The investigators noted that if the hooks between column and slab were extended, they would have saved the day. That being said, I don't see hooks on a continuous wall or footing to act in the same way as in a punching shear failure, so maybe it's not necessary. But then again, you don't want to be mixing dowel sizes on a jobsite, so just use the longer ones.
I'm not following. Can you explain this again?
RE: Rebar 90 degrees hook length
If this dowel is intended to work in shear for some sort of lateral load than the calculation should follow the shear friction provisions of ACI (if this is IBC design). You could intentionally roughen the top surface of the walls to get more capacity out of this joint.
RE: Rebar 90 degrees hook length
ACI 318-14, 25.4.10.2 exception (b) triggers for dowel conditions as these are for shear friction transfer and need to develop Fy on both sides of the slip plane.
ACI 318-19, 25.4.10.2 amended exception (d) to include hooked reinforcement.
RE: Rebar 90 degrees hook length
In that case, though, I don't think even #4 can be fully developed. I ran a quick calculation using 25.4.3.1 and I got 9.5" for 4000 psi concrete.
RE: Rebar 90 degrees hook length
I'm not sure what you mean by "double-counting". It does perform 2 functions, if that's what you mean. the hook would theoretically develop sufficient tension capacity for the vertical leg, and the extension gives it sufficient development to resist the moment in the footing. I don't se it as being substantially different than a straight bar extending through a tension zone - there's tension force pulling both directions away from the middle.
In the case of your dowels, if the dowel is supposed to carry moment around the corner, the horizontal leg of the dowel has to have a lap length to the top horizontal bar past the point where both bars are needed to resist the negative moment in the slab.
RE: Rebar 90 degrees hook length
In general terms, both are fine ways to build a foundation (though in the 2nd one my footing bar should probably have hooks)
RE: Rebar 90 degrees hook length
RE: Rebar 90 degrees hook length
@Greenalleycat Thanks for sketching it out! I get what you mean. And if the retaining wall is taller, that big piece can still function as a dowel.