This is how I'd like to pipe in a new heat exchanger into the existing building system. The pump shown is variable speed. I'm concerned that the higher pressure HWS upstream water will push more water through the pump than required when the pump is running at low speed. Do you think this will be an issue? Curious if the pump will "resist" the additional turning of the impeller if the upstream pressure is trying to push water through, when it's running. Thanks in advance!
RE: Pump Upstream Higher Pressure Issue
Cavitation, if a centrifugal pump.
Energy being driven into the motor which needs to be dissipated in a breaking resistor.
Cavitation will be avoided if a positive displacement pump like a progressive cavity pump is used.
The energy problem is easily solved by using a 4 quadrant capable VFD, Including either a breaking resistor and /or a VFD capable of returning energy to the power distribution system.
The valve can be kept wide open unless the pump is unable to control the flow rate.
I realize this is a very non standard pump selection for an HVAC application, but I have used it in another application.
RE: Pump Upstream Higher Pressure Issue
But what does the valve CV control on? If flow is being controlled by that why are you bothering with a VFD? What did it control on?
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Pump Upstream Higher Pressure Issue
Each will react to changes caused by the other and you'll have induced oscillations.
RE: Pump Upstream Higher Pressure Issue
I believe I did think of a solution to this; a pressure sustaining valve after the control valve and setting it to match the HWS pressure. That way it makes the downstream pressure and upstream pressure of the pump the same.
RE: Pump Upstream Higher Pressure Issue
What exactly are the pressures here?
So how much flow can you get if you simply connect the HWS to the HWR via the HX? 25% of what you need? 50%?
How much more pressure do you need for the flow? If say the PD between S and R is 15 psi but you need 60 to get the flow through the HX then fair enough, but without some data here we're a bit stumped.
Why is the pump variable speed? does it go through some sort of controller measuring the difference between set point of the air and the actual air temp?
The back pressure valve idea would work but means more power used by the pump.
And most people would be confused by a Control Valve which just is an isolation or MOV on/off valve. Control valves usually control.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Pump Upstream Higher Pressure Issue
What are pressures in the loop and what pressures needed for design HX flow? Will loop pressures be stable or fluctuate? Will required HX flow be variable or constant?
RE: Pump Upstream Higher Pressure Issue
What are the supply and return temps of your BLDG HW mains?
What is the rough flow in the Bldg HW mains?
What is the flow of your new pump?
What supply and return temps do you want on the other side of the heat exchanger?
RE: Pump Upstream Higher Pressure Issue
Pressures: trying to get that information but it's likely around 30 psi +/- 10 psi. I agree that it would be good to just connect it directly without a pump but then we would have to buy proportional control valves since we need to dial in the temperature. So I'm trying to make the pumps work if possible, which will be controlled with a 0-10 VDC input.
Why the pump is variable speed: see diagram, we're trying to maintain a 70 °F discharge air temperature from outdoor air that varies throughout the year between -10 and 100 °F.
Sorry for the control valve symbol confusion, wasn't quite sure how to show it.
"CV" (now "MOT") is on/off, yes. Loop pressures could fluctuate slightly, yes. But I believe the BLDG main pumps are set up to maintain constant pressure. HX flow to vary to maintain discharge air temperature.
S/R temps for bldg mains: 140/120. Flow will vary, there are 6 different locations across the building where this setup with occur. 9 pumps, each slightly different flow but all around 20-30 gpm. fan coil side of HX, looking for 138 supply and 108 return.
RE: Pump Upstream Higher Pressure Issue
RE: Pump Upstream Higher Pressure Issue
I was hoping your fan coil supply temp would be significantly lower. I was going to suggest pulling both your supply and return branches off the Bldg return, so that you would have no pressure differential created by the main building pumps. Obviously, that can't be done here.
You mention 30 psi +/-10. This is the pressure differential that you are expecting in the bldg mains? Measured where? That sounds high....not knowing any of the particulars. What else is on the building system aside from these heat exchangers?
RE: Pump Upstream Higher Pressure Issue
RE: Pump Upstream Higher Pressure Issue
RE: Pump Upstream Higher Pressure Issue
RE: Pump Upstream Higher Pressure Issue
If the pipe pressure is enough, you could use a modulating PICV. If it isn't, you use the on/off valve and modulating pump. but the pump is only needed if you lack the pressure.
Your control schematic lacks the temperature sensors. and is your on/off valve really controlled by 0-10V signal? that typically would be a digital output on the controller.
RE: Pump Upstream Higher Pressure Issue
Unfortunately, the pressure is not quite high enough to do it with a modulating valve. The on/off valve is controlled by the pump; if it runs, the valve opens, if it stops, the valve closes. The variable speed pump is run off of a 0-10V signal from the discharge air temperature sensor.
RE: Pump Upstream Higher Pressure Issue
As far as the system you are speaking of that was somewhat popular in the late 90's. I think it was a called a tri-pipe system and it was actually a patented system. Can't say I'm a fan of them. EVERYTHING is potable water rated so selection of components is a pain. On cooling side they are actually tied to the domestic cold water and the fire-suppression system piping. I've only modified them, never designed one, and I don't like modifying them.
RE: Pump Upstream Higher Pressure Issue
Never heard of that combined domestic/heating system. Seems like it would be plagued with problems when there isa large domestic load. I assume that the domestic outlet pipes are connected to the HW Supply lines. That could leave very little flow in the return lines at times and erratic pressures it would seem??? I don't want any part of such a system.