Pile Cap Bottom Reinforcement Sitting on Piles

Pile Cap Bottom Reinforcement Sitting on Piles

Pile Cap Bottom Reinforcement Sitting on Piles

(OP)
There has been a back-and-forth in our office and with a client engineer about resting the bottom layer of a pile cap's reinforcement directly on top of the piles. To be specific, we have a 2'-6" thick pile cap with 24" pipe piles sticking up 4" and a 1/2" cap plate on them. We are showing that the reinforcement is to be 4 1/2" clear of the bottom, allowing the construction crew to essentially use the piles as big standees.

Your thoughts?

-5^2 = -25 winky smile

RE: Pile Cap Bottom Reinforcement Sitting on Piles

Interesting question. The clip below is from CRSI's pile design guide. It shows 3" cover from the top of the piles to the rebar. To my knowledge, nobody does that for concrete piles. There, we hope that the pile concrete below the bars provides adequate passivation for corrosion etc. Is the setup still alright for durability when the pile is steel? It's pretty easy to imagine water getting up there.

All that is not an "answer" of course. But, then, you did ask for thoughts...

RE: Pile Cap Bottom Reinforcement Sitting on Piles

I usually specify for 2" consider the top of the piles a formed surface. It seems like you want encasement of the bars for better durability

RE: Pile Cap Bottom Reinforcement Sitting on Piles

We typically spec the rebar in footings to be 2" clear from the top of steel H-piles. Whether that actually happens when they build it, is anybody's guess. Our piles are typically embedded 12", just in case they're subjected to a substantial moment, due to scour or seismic.

RE: Pile Cap Bottom Reinforcement Sitting on Piles

(OP)
Thanks for the feedback.

We commonly have not left any gap there. So that we don't belabor the point with the client, we'll be moving ours up...

-5^2 = -25 winky smile

RE: Pile Cap Bottom Reinforcement Sitting on Piles

When you “move it up”, just be sure the required effective depth is not compromised.

RE: Pile Cap Bottom Reinforcement Sitting on Piles

The gap should be at least the bar diameter!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close