This is a topic of confusion in my office because of the way the two codes are written. Hopefully someone can enlighten me...
AS 1170.0
In AS 1170.0, the earthquake load combination is:
1.0 x EQ + 1.0 x G + ψE x Q
To my mind, the above equation makes complete sense. The EQ force is based on the unfactored mass of the structure (allowing for some permanent component of live load).
The 'load factor' for the EQ loading is basically built into probability factor kp in AS 1170.4, and is calculated based on the unfactored mass.
The important thing to note in my opinion is that this 'load factor' scales up the magnitude of the EQ acceleration, but not the mass of the structure.
It then makes sense that the dead load factor should also be 1.0 because we are dealing with acceleration effects on the nominal (unfactored) mass of the structure. It would seem wrong to consider the unfactored mass of the structure for EQ effects, but then to artificially scale the mass up or down for gravity effects.
But --- this is exactly what AS 5100.2 seems to suggest.
AS 5100.2
Let's take a mostly concrete bridge (for simplicity), so the EQ load combination according to AS 5100.2 is:
1.0 x EQ + [0.85 or 1.2] x Concrete Dead Load
At first glance, this would suggest that we have to calculate the EQ force based on the nominal mass of the structure (hence the 1.0 factor), and then scale up or down the gravity effects (by a factor of 0.85 or 1.2). This approach has the obvious problem that only one of the mass-derived loads is scaled while the other remains unchanged, which is inconsistent. Unlike the probability factor kp, which is effectively a ULS factor applied to the EQ acceleration, the 0.85 or 1.2 dead load factors instead scale up the mass of the structure (not the gravitational acceleration).
Or - is it saying that we should first scale the mass of the structure (by a 0.85 or 1.2 factor, say), and then apply both the EQ and gravity effects on this scaled mass? This approach is more consistent in that both of the mass-derived loads are scaled by the same amount, but we are now effectively applying a second load factor onto the EQ effect (i.e. on top of the probability factor kp in AS 1170.4).
My personal opinion is that AS 5100.2 is simply wrong and that this particular load combination has been overlooked. There are plenty of other examples throughout the AS 5100 series where obvious errors have been overlooked and unchanged for several years without revision. The AS 1170.0 approach, in my mind, is consistent and logical.
AS 1170.0
AS 5100.2