Cantilever steel beam at column

Cantilever steel beam at column

(OP)
When you design a cantilever steel beam with moment connections at both sides of the column,  do you assume part of the moment goes to the column (due to relative stiffness of the beam and the column) and design the column for that additional moment??  Please advise. For some reasons, we have been assuming the beams are having two pinned connections, and designed columns with vertical load only. Now, I am worried...  

RE: Cantilever steel beam at column

by definition, a cantiliver is an element with one end fixed and the other end free, therefore you have Moment in the fixed end, so, the element providing support for the cantiliver it is in this case, your column, and has to be design to both the axial loading and the moment by the cantiliver...

RE: Cantilever steel beam at column

Why do you think a beam analyzed as pinned-pinned-free is not valid?  If your connection is free to rotate, a moment should not develope.  I certainly agree with taking precautions... however, a cantilever is not only bound by one definition - "one end fixed and the other end free."

RE: Cantilever steel beam at column

Don't understand why the moments at column ends should depend on the relative stiffness of beam and column, as a cantilever beam is statically determinate and should not influence by its stiffness the load distribution in the rest of the structure: perhaps you should clarify your structural scheme.
Anyway in my opinion you are always safe if you calculate moment connections as if they were pinned, provided you are not in a high fatigue environment and you take the same assumption in all the structural checks performed on the element. However this would of course be a waste of effort in building a moment connection that is not used as such...

prex

http://www.xcalcs.com
Online tools for structural design

RE: Cantilever steel beam at column

If it is stub beam projecting from a column it must have a fixed connection (i.e. able to develop a moment) otherwise it will fail. You should not let all the theory get in the way of what actually happens. You should design the column for the additional moment due to the load from the cantilever beam and make sure that the plate, bolts or welds and the local column capacity are good enough. Always put stiffeners in so that the flanges of the beam are continued into the web of the column.

RE: Cantilever steel beam at column

prex - you are right that a cantilever is a statically determininate element...but the moment at the end of the cantilever then extends out to whatever will take it.  In this case, you have two - the remaining beam and the column.  If the connection is fully moment resisting for both the beam and the column, then the cantilever moment will be distributed to each according to their stiffness.  

If the cantilever/beam connection to the column is not designed to take moment, then you could assume that all the cantilever moment extends into the beam.

However, very few connections of any kind are truly "pinned" so I would include some column moment in my column design.

RE: Cantilever steel beam at column

I concur with JAE. In such situations, we must consider the difference between what is on paper and what actually occurs.

I might add, however, that the answer to this question relys primarily upon the connection of the column to the beam. Does the connection allow internal distortion, thus preventing the column from participating in the moment distribution?

RE: Cantilever steel beam at column

JAE

I agree with your first statement. If the inner beam is moment-connected with the column, the moment from the cantilever will be shared by the column and the inner beam.

But I am afraid your second statement is not correct. If the column to inner beam connection is a shear connection, the moment will be totally resisted by the column only. The logic is as below.

First of all the cantilever beam has to be moment-connected with the column, as otherwise the cantilever will become unstable. Hence the moment will first get transferred to the column at the joint. If the adjacent beam is not having a moment connection with the column, the inner beam end will tend to rotate and only the bending stiffness of the column will contribute to the resistance.

The inner beam will get the moment only if either the beam has a moment connection with the column or if the cantilever beam is continuous over the column and connected to the column at its bottom flange through a bearing plate. In the latter case, the column will act like a knife-edge without taking any moment from the beam.

RE: Cantilever steel beam at column

trilinga - I agree with all that you say.  My second statement, however, was not directed at a shear connection between the main beam and the column, but rather a connection where the whole beam extends over the column (the column perhaps has a cap plate that is simply bolted to the bottom flange of the cantilevered beam.  In that case, the moment will most certainly extend directly through beam, past the column.

But a bolted cap plate to a bottom flange has SOME capacity to accept moment from the cantilevered beam above...just difficult to determine.  

RE: Cantilever steel beam at column

You are right JAE. That is precisely the arrangement I have mentioned in the last sentence of my post. But, it is not posible when the column extends above the beam level. In such case the adjacent beam has to be either moment-connected or shear-connected to the column resulting in the corresponding moment transfer mechanism.



RE: Cantilever steel beam at column

(OP)
Thanks everyone for your input. Usually if the cantilever is short or the beam is a lot stiffer than the column. The moment distributed to the column is small, thus it's safe to ignore. However, in my case, I have a 10'-0" cantilever and the column is a W14x500. I have moment connection (bolted or welded) at the cantilever and the back span.  The mega column tends to suck up a huge amount of moment.. which was not anticipated at the beginning. Anyway, I have run a computer analysis on the system and re-designed my column with the additional moment. Fortunately, it has extra capacity for that. Phew. Thanks everybody.  =)  Have a nice day.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close