VFD Under Voltage Fault
VFD Under Voltage Fault
(OP)
Hi all,
I've had 2 single phase to 3 phase 2.2kw 10A VFDs for several years now with no issues. One on my lathe, one on a mill.
Recently got an INTERMITTENT error of UU undervoltage (on both VFDs). It can run fine for ages then suddenly trip. Sometimes under load, sometimes not. Tried with different motors, makes no difference. I wired up a new (3rd) vfd of same model to the lathe and works fine. Sometimes before it trips you can hear the relay clicking randomly. I believe this relay controls the input single phase voltage charging the capacitors with rectified DC voltage and shorts the high power resistor to stop the charging when full.
Mains voltage is fine and on 32amp breaker.
Unplugged all other equipment on the same ring. No difference.
Opened the VFD and checked the capacitance of the 2 820uf caps which gives approx. 1476uf for both which is low but within 10%.
Unsoldered relay and this seems fine. Coil resistance is ok I think and switches with 24v appied over the coil.
Unsoldered the rectifier and seems to test ok with multimeter.
Checked the resistor on both VFDs, one about 152ohm and the other 158ohm. I assume this should be 150ohm???
I replaced the resister (158ohm reading) with the (152ohm) resistor and put the VFD back together and it worked flawlessly last night. Tried this morning and tripped again. I think this may be due to the motor struggling because I had the lathe setup with the steady a bit too tight. Now it tries to run the motor and just trips again.
Is this because the resistor is getting burnt out and increasing in resistance when hot preventing the capacitors from charging fully (quick enough)?
Model of the VFD is Ecogoo 9100. Manual attached.
https://youtu.be/FHZwKex2w-8
https://youtu.be/uIVjzKOz5qs
Please excuse Mrs moaning in the background :)
I've had 2 single phase to 3 phase 2.2kw 10A VFDs for several years now with no issues. One on my lathe, one on a mill.
Recently got an INTERMITTENT error of UU undervoltage (on both VFDs). It can run fine for ages then suddenly trip. Sometimes under load, sometimes not. Tried with different motors, makes no difference. I wired up a new (3rd) vfd of same model to the lathe and works fine. Sometimes before it trips you can hear the relay clicking randomly. I believe this relay controls the input single phase voltage charging the capacitors with rectified DC voltage and shorts the high power resistor to stop the charging when full.
Mains voltage is fine and on 32amp breaker.
Unplugged all other equipment on the same ring. No difference.
Opened the VFD and checked the capacitance of the 2 820uf caps which gives approx. 1476uf for both which is low but within 10%.
Unsoldered relay and this seems fine. Coil resistance is ok I think and switches with 24v appied over the coil.
Unsoldered the rectifier and seems to test ok with multimeter.
Checked the resistor on both VFDs, one about 152ohm and the other 158ohm. I assume this should be 150ohm???
I replaced the resister (158ohm reading) with the (152ohm) resistor and put the VFD back together and it worked flawlessly last night. Tried this morning and tripped again. I think this may be due to the motor struggling because I had the lathe setup with the steady a bit too tight. Now it tries to run the motor and just trips again.
Is this because the resistor is getting burnt out and increasing in resistance when hot preventing the capacitors from charging fully (quick enough)?
Model of the VFD is Ecogoo 9100. Manual attached.
https://youtu.be/FHZwKex2w-8
https://youtu.be/uIVjzKOz5qs
Please excuse Mrs moaning in the background :)
RE: VFD Under Voltage Fault
That would also explain why both drives trips at the same time.
Best Regards A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: VFD Under Voltage Fault
Muthu
www.edison.co.in
RE: VFD Under Voltage Fault
I think relay is dead (contacts burnt) and charging resistor reamin in circuit so voltage at inverter input drop below UV limit and trip.
RE: VFD Under Voltage Fault
RE: VFD Under Voltage Fault
@ edison123, I can't find any loose connections.
@ iop95, I posted a video on youtube showing the voltage over the caps.
@ FacEngrPE, I don't think I have access to such equipment other than rigging something up on an ardruino? Not sure what voltage they can take :)
RE: VFD Under Voltage Fault
If your drive specifically states it is rated for a single phase input, then the OTHER thing that affects the DC bus ripple is load. So if, even for brief moments, your load is demanding more torque (ergo more current) and the VFD is attempting to deliver it, then that can result in an under voltage trip due to it causing high DC bus ripple. If that increase in demand current from the motor also corresponds with a dip in line voltage, which can easily happen on a single phase source, then the UV trip is all but guaranteed.
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
RE: VFD Under Voltage Fault
Seems that DC bus capacitors are at very low value... check them.
But also check if contacts relay are realy closed (may measure voltage at these contacts - must be near zero after relay close).